Discuss Rcd tripping problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Hi guys here's an update'ive been on site today and done a thorough inspection and found that IR between earth and disconnected neutrals all fine(2 circuits 22 Meg all the others 299

One thing that has come to light is that the over head line has recently been changed to pme or pmb,not sure which .
But the overhead line now has a earth cable running from what I believe to be neutral to an earth electrode,which is about 30 yards from my incomer
Ive checked linked N & E at my supply and all ok,wondered if I was getting some sort of leakage to the suppliers neutral which is connected to an earth electrode in close proximity.
finally the property used to be a TT system and electrode still in the ground but not connected,also water supply in lead I think
oh and I've changed the Proteus RCDS for Hager
So wait and see!!!!!!!!!
 
No the overhead supplies PME N-E connection will have no affect on your RCD tripping problem. Depending on the Ra of the existing rod it might be a good idea to reconnect the rod to the MET. Don't bother if the Ra is way over 10 ohms.

22 Meg ohms equates to 22 million ohms, so you don't have a problem there either. So if the problem remains you have more checking and testing to do!!
 

Reply to Rcd tripping problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
826
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock