Discuss RCD tripping when switching oven isolator off in the UK Electrical Forum area at ElectriciansForums.net

streamer

-
Esteemed
Arms
Reaction score
435
Hi all.
I was called to a house recently where the occupier reported that when they turned the oven isolator off the RCD would trip.
So I tried it and that's exactly what happened. There was nothing switched on on the oven at the time. When the oven is on it works fine.
It is an integrated oven on a dedicated 16 amp circuit. Circuit tested fine in all respects and a ramp test on RCD showed it tripping at 24 mA.
They have to turn the isolator off when not using the oven as they have a son with learning difficulties who sometimes turns the controls on the front of th oven.
Any ideas what the cause might be?
Thanks.
 
Did you try an earth leakage clamp.on the circuit? It is possible that there is a spike when turning it off which is pushing an already close RCD over the edge, it's a long shot but I have seen it happening
 
as post #4. try replacing the isolator before the head scratching.
 
Edit as previously mentioned. Have a look at the Beama RCD guide, section 9.3. Could be a possibility
 

Attachments

  • RCD Handbook (Dec 2010) (6).pdf
    4.8 MB · Views: 27
Replace the DP switch with one which makes the neutral before the line and breaks the line before the neutral. I think MK cooker switches operate this way.

Understandable for a 3ph DB main switch for example.

However, this shouldn't in theory effect a single phase load. There isn't a difference in current draw, by switching line or neutral.

Unless the switch is faulty and is sending some current elsewhere.
 
Understandable for a 3ph DB main switch for example.

However, this shouldn't in theory effect a single phase load. There isn't a difference in current draw, by switching line or neutral.

Unless the switch is faulty and is sending some current elsewhere.

Beama talk about 'Double pole switching within the fixed wiring is known to produce a strange phenomenon whereby switching OFF a double pole switch supplied through an RCD can cause the RCD to trip.' in their RCD Handbook.

So there must be some substances to it.
 
Beama talk about 'Double pole switching within the fixed wiring is known to produce a strange phenomenon whereby switching OFF a double pole switch supplied through an RCD can cause the RCD to trip.' in their RCD Handbook.

So there must be some substances to it.

The only thing I can think of, is it causing some from of capacitive spike in the cable.
 
Re #14: The sequence of switching of the line and neutral does affect the changes of potential differences of the line and neutral conductors with respect to earth - and because of this there is the possibility of transient current flows through the line and neutral conductors distributed capacitance to earth which does create a differential current through the RCD. Plot out the changes of potentials/currents for the equivalent circuit and you will see what happens - which is why in earthed neutral systems single phase DP switches are make N first break N last - so N conductors remains at earth potential - ie do not momentarily jump up to Line potential then down to zero to avoid nuisance tripping of RCDs.
 
Re #14: The sequence of switching of the line and neutral does affect the changes of potential differences of the line and neutral conductors with respect to earth - and because of this there is the possibility of transient current flows through the line and neutral conductors distributed capacitance to earth which does create a differential current through the RCD. Plot out the changes of potentials/currents for the equivalent circuit and you will see what happens - which is why in earthed neutral systems single phase DP switches are make N first break N last - so N conductors remains at earth potential - ie do not momentarily jump up to Line potential then down to zero to avoid nuisance tripping of RCDs.

Yes, as soon as I stopped an actually thought about it, I realized what could happen.
 
Had this on a board change I did a while ago.
Customer reported rcd tripping when they turned the cooker off.
I must say this was the first time I have come across this particular problem
 

Reply to RCD tripping when switching oven isolator off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
708
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock