Hi all,

I am trying to diagnose the following problem.

After coming back from holiday, we noticed that our RCD keeps tripping a few minutes after our kitchen lights have been turned on. If the kitchen lights are kept switched off, then everything is ok.

The lights were GU10 spotlights connected to a dimmer switch. Replaced the dimmer switch with a trailing edge dimmer and replaced the GU10 with dimmable LEDs ... and the problem is still present.

Any ideas what this could be and how to test the fault ?

Could there be water somewhere in the ceiling cavity ?

Any advice is appreciated !

Many thanks !

Harpoon
 
Its been a fairly wet week across Britain so damp on that part of the lighting circuit might be an issue. Seeing as you have changed the switch and lamps its pointing towards the wiring instead. Basic Insulation Resistance testing would find the fault but remember to disconnect your brand new accessories. This is simple fault finding for any decent Electrician, call one.
 
Yep, I agree with Will, the reason I asked if low voltage or mains voltage was because if they had been low voltage, the transformer would have come into play and may have been faulty, but as they are mains this does not apply.
How old is your wiring?
 
Hi guys,

The wiring is ~3 years old ... part of a kitchen extension.

I tried to localize the dampness by only fitting certain lights ... hoping a certain combination will be OK ... but no luck.

There are 10 LED downlights ... had 5 on and 5 off, still tripped
Swapped them around ... still tripped
Fitted only 3 LEDs ... still tripped.

Looks like that is about all I can do now.

Will be calling an electrician in the morning ...
 
I have not found any dampness ... but thought it may be the reason ?

The ceiling is near a bathroom which may be the culprit ... though we cannot see any water marks anywhere ...
 
RCDs are designed to disconnect the supply if a fault occurs which could kill you, do you really think that it is sensible course of action to randomly replace bits and pieces and just keep resetting the RCD?

You could feasibly end up damaging the RCD so that it no longer trips, then you'll be left thinking youve fixed the fault when all you've done is hidden a fault which could kill you or on earth of your family.
 
I guess I wasn't thinking ... just trying to localize/understand the problem.

Like i said ... I will be calling the electrician tomorrow ...
 
Has anyone come across this before ? ... i.e. RCD only trips after the circuit has been switched on for a while ... does it make sense ?
 

Reply to RCD trips a few minutes after lights turned on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
828
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock