Hay

I cant do an RCD test

When i press the test button the rcd trips before i can get a reading ??

I hope you don't mean you are pressing the test button incorporated on the RCD.


Sent from my iPhone using Tapatalk
 
Is it on "soft" test thats if it has that option?
is it a loop test? because an earth loop impedeance test will cause RCD to trip
 
Last edited by a moderator:
could well be a "cooked" rcd - ramp test it and also check your tester on another rcd. A megger 1552 will show "TRP" if the rcd is faulty and not behaving. Have seen this when the load from the mcbs well exceeds the max cabability of the rcd.
 
my dilog gives a blank screen and just beeps at me then say M Ohm!! when batteries are low as its **** and i change them every bloody 3 weeks!!

What make testers have you got? My megger mft seems to get through them fairly quick, although have started turning them off between tests lately and this seems to help.
 
Hay

I cant do an RCD test

When i press the test button the rcd trips before i can get a reading ??

Ah! You are not doing what I think you are doing are you?!

The "TEST" button on the RCD is for manual mechanical testing only - you do not press this when carrying out the X1 and X5 tests with your meter.
 

Reply to RCD trips to fast on test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
556
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
478
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock