For a cable likely to be totally surrounded by thermal insulation over a length of more than 0.5 m, the current-carrying capacity is to be taken as the current-carrying capacity for that cable clipped direct to a surface and open (Reference Method C) multiplied by a derating factor (
1c005-37_ileqn1113.jpg
) for thermal insulation. In the absence of more precise information,
1c005-37_ileqn1214.jpg
is to be given a value of 0.5.

Tabulated current-carrying capacities for various types of cable installed in a thermally insulating wall or above a thermally insulating ceiling - the cable being in contact with a thermally conductive surface on one side are given in Appendix 4 of BS 7671.

Regards

Dichroic
 
It'll either be method 100 or 101 depending on the thickness of the insulation, i.e less than 100mm = method 100, more than 100mm thick = 101.
 

Reply to reference methods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock