For a cable likely to be totally surrounded by thermal insulation over a length of more than 0.5 m, the current-carrying capacity is to be taken as the current-carrying capacity for that cable clipped direct to a surface and open (Reference Method C) multiplied by a derating factor (
1c005-37_ileqn1113.jpg
) for thermal insulation. In the absence of more precise information,
1c005-37_ileqn1214.jpg
is to be given a value of 0.5.

Tabulated current-carrying capacities for various types of cable installed in a thermally insulating wall or above a thermally insulating ceiling - the cable being in contact with a thermally conductive surface on one side are given in Appendix 4 of BS 7671.

Regards

Dichroic
 
It'll either be method 100 or 101 depending on the thickness of the insulation, i.e less than 100mm = method 100, more than 100mm thick = 101.
 

Reply to reference methods in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

If cable is run through holes in joists, then turns through 90 degrees, clipped to the joist, then clipped to the brick wall as itvdrops to the...
Replies
0
Views
231
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
637
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
650
Hi Guys Is there a reason why installation ref method B (in conduit or trunking on a wall) not listed as an allowed installation method on the...
Replies
3
Views
839

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock