Discuss Remedial work after EICR in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,018
Ive been asked to quote for remedial work for local village hall after another company flagged up some C2's along with C3's

The C2's are basically add rcd protection to the socket circuits...fair do's
Now why are they a C2, but RCD on the lights isn't mentioned at all? not even a C3

They say smoke detectors do not meet new scottish law... Huh?? Will that be the new scottish law for DOMESTIC properties? They gave this a C3
Shouldn't have been coded at all. Maybe just a note. Only need to code the fixed wiring, not the detector on the end.

They have ticked the supply characteristics as 1 phase, 3 wire.... when i know its a 3 phase board... there's just no 3 phase equipment.
They've used the circuit chart numbers R1,Y1,B1,R2,Y2,B2... etc.... that should have given a clue.


Looks like its add a few RCBO's to the sockets, update the smoke detectors, and change an emergency light as there's one with heat damage.
 
Now why are they a C2, but RCD on the lights isn't mentioned at all? not even a C3
Possibly because it's not domestic?
They have ticked the supply characteristics as 1 phase, 3 wire.... when i know its a 3 phase board... there's just no 3 phase equipment.
That's concerning.

If it were me I wouldn't change the smokes unless there's a compelling reason to, and in my covering letter I'd say the installation is now satisfactory and that item <whatever> is not in scope of an EICR.
 
Would you need AFDD protected circuits as recommended for Certain areas of particular public risk.
For an EICR, my view is they should only be C3'd if the building is a HMO, Student Accommodation, Care Homes or a HRRB.

If it was a new installation or new circuit in a village hall then it might be considered under the "you might want to do this" part but in all likelihood it would be quickly rejected for cost reasons.
 

Reply to Remedial work after EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock