Hi.
An electrician isn't my day job but I qualified on one of those 'quickie' courses a couple of years ago, thus I am competent yet rusty on some aspects.
My conundrum is that a consumer unit needs upgrading. However, the CU is situated in a low cupboard on a narrow (right hand) wall, it just fits and awkward to get to.
A new (amendment) CU is obviously much larger, but would fit comfortably on the adjacent wall some 40cm away.
My question please, to the venerable, is: Would it be acceptable to replace the old CU with a junction box housing, and to run the various twin & earth cables from here to the new CU nearby?
Many thanks for (polite) replies!
 
Providing you used the correct enclosure/connectors, and the install was up to current standards, and the DNO was prepared to move the supply to the new proposed position, and if the cost of moving the DNOs equipment was cost prohibited, and you used the correct install method and equipment for the supply from the existing head to the new CU position, I see no reason why not.
 
Similar to this...(not my job BTW). I don't think the DNO equipment needs moving as it's only being moved 400mm and no distribution circuit. Looks like the OP is moving the position as a new amm3 style box won't fit in the existing space.

IMG_1653.jpg
 
What you are suggesting is an option, but I would avoid having to extend the tails in said enclosure .........

The last time I did something like this, I used a Henley block next to the old board for the tails and an external met next to the Henley...
 
Just a note, if you do use din rail connections. Connect the CPCs in normal din rail connectors NOT the earth ones as shown, as this will effectively connect all the CPCs together across the Din rail and make testing difficult if disconnecting at the DB terminals
 
Whow, thank you Vortigern for your swift reply and thank you all for your replies, love the photo Leesparky, helps a lot.
Yep, no need to move the DNO because, unlike the photo the new CU will be at the same horizontal level as the old one, (or 'head' as it will become,) but on the adjacent wall and so will become actually slightly closer to the DNO equipment. However, it does mean that I will need to run the extended cables externally between the units. (Just wish it was at head height and not under a low cupboard!)
Nice thought Wilko about using RCBOs I'll have a scratch of the head and get my tape measure out.
- and take a gander at the various types of din rail connectors.
Thank you all again.
 
If you are going to get a new CU how about installing an isolator after the meter?
 

Reply to Renewing consumer unit - no space in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
902
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
845
HI My flat just failed the EICR because there is no RCD in the consumer unit. There is no space for a new RCD as the consumer unit is full. Do I...
Replies
18
Views
2K
Hi all, new to posting but been reading for years. I inherited a house from my grandmother who passed in 2021, I intend to renovate and rent out...
Replies
97
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock