Discuss Replacing broken junction box outside in the UK Electrical Forum area at ElectriciansForums.net

Steve T

-
DIY
Reaction score
117
Hi

I’ve got a junction box outside which is cracked. It has 3 1.5mm SWA cables going into it.
I’m planning on replacing it with a Wiska 308 box, with piranha earth nuts. In the old junction box the SWA was not earthed-banjos attached but no earth fly lead.
I’ve got two questions about installing the new junction box:
1) What CSA should the earth fly lead from the piranha earth nuts be?
I’m guessing it should be the copper equivalent to the CSA of the steel armour, but I’m struggling to find this information!
2) Would you put ‘magic gel’ in the junction box, in case of condensation?
Thanks for any replies
 
Last edited:
Thanks, what CSA cable should I use to connect to the earth bar?
I’m struggling to find out what the copper equivalent is to the CSA of the steel armour.
 
You will have a lot of fun terminating five different cables into a 308 JB without it looking like a rats nest.
The wiska boxes are designed not to accept standard components for SWA so you have to buy the earthing bar; that does not seem to be available for any other size box than the 308, though I have probably just missed them.
The copper equivalent of the armour is about 6mm², but the maximum size you will need will be the csa of the cpc for the circuit, if the armour is is the cpc then go with Baker1988.
 
The armour is not the Cpc, there is a cpc inside the cable. I will use 1.5mm cable as the fly lead, and I might go for the wiska 407 instead to give myself more space. It has also got similar earth bars available.
 

Reply to Replacing broken junction box outside in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m a DIYer I am trying to replace an outside PIR lamp which is connected to an internal fused switch in the hall. Removing the cover of the...
Replies
4
Views
933
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Hi, I recently saw a post on Screwfix forum, but it has not been answered and because I have used the same set up would like to check that...
Replies
2
Views
2K
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the...
Replies
29
Views
4K
I think I'm being dim here, but it's been a long day and I won't be able to sleep with this rolling around in my head - so can anyone help me out...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock