Hi all, planning to replace my electric ceramic hob for an induction one.

Current ceramic hob is:
Baumatic B12SS - 230v/400v 3N 50/60Hz 6kW 26.1A, min fuse protection rating 30A.

The current setup is as follows:
CCU>1xB32 MCB>connected to 2x red cooker switches:
  • Switch 1: connected to hob above
  • Switch 2: connected to 2x electric Neff ovens, EACH rated 230/240v 50Hz 3.6kW 16A (models B6774N0GB and B1524N0GB)

Question 1) If the B32 MCB is 32A rated, doesn't that mean that it can support up to a max of 230x32=7.4kW, and if so, 6kW (hob) + 3.6kW (oven 1) + 3.6kW (oven 2), far exceeds the maximum tolerance of this single MCB, when all 3 appliances are at full power? Granted, only on very rare ocassions I have used both ovens plus 4 hobs (Christmas...), and nothing actually tripped. Have I miscalculated the tolerance; is this a safe setup for these appliances?

Question 2) Considering swapping the above hob for 32A wired 7.4kW rated Siemens Induction EX675BEB1E. Is the above setup suitable for a direct swap?

Many thanks

Rupert
 
you need to take diversity into account.this means that the elements willnot all be drawing juice at the same time, except when initial switch on ( thermostats switching on and off). a 32Acircuit with6.0mm cable has been good for coooking appliances upito 15kW for donkeys, so just connect your new hob. if in doubt, get a local spark to test the circuit.
 
As above. With diversity, I have your old set up as drawing 38A, and the new one as 40A. As the old set runs ok, can't see the new one not either. If it was a new install, you would probably have two 32A supplies or one 40A.
 
Many thanks guys. For added info, the CCU is 5 meters apart from both red switches (in case this helps).
CURRENT setup on single 32A MCB: 6+3.6+3.6 = 13.2kW
NEW setup on single 32A MCB: 7.4+3.6+3.6 = 14.6kW

Please forgive my ignorance, checking on NEW setup:
14.6/230 = 63.5A (no diversity applied)
10A + 0.3 x 53.5 = 26.03A (with diversity)

Are my calcs above OK? Is this safe basically because 26.03<32? But what happens when I run all 4 hob zones plus an oven (which is something I do on an almost daily basis)? Will the connection not take it?

Thanks again for your time.

R
 
Hi - as you’ve calculated, it is possible to overload the circuit with those appliances. The next question - how likely is it? If you were running a restaurant or some such then I’d say it’s not ok and a new circuit is required. If you envisage firing up all 3 appliances together, then for peace of mind I’d run a second circuit if that’s possible.
 
Interactive User Manual - https://media3.bsh-group.com/Documents/siemens.html?matNumber=9001330662&lang=en

The Induction Hob you are buying has a 'power manager' function which enables the installer or user to set an upper limit on the total power consumed - automatically. So with PM off, the factory setting is for a total inductive heating output of 7.4kW and no more. By selecting PM - look at the link - you can see that the total power can be lowered to suit lower capacity supply (down to a 13A plug). Of course this would mean that when all hobs are in use at the same time on high/full power settings it may take a little longer to first heat up the pans and its contents because a smaller amount of electrical power is spread over the same number of hobs.

Take a look at the reference for further information and setting 'C7'.

So, I would connect up to your current supply and if there are problems you can tweek the maximum power limit. This is what I did for my brother-in-law's new kitchen install and he likes cooking for the 5000 and no-one waits overly long.
 
Last edited:
Have you actually used yet an IH? They are a MArmite appliance if you get my comparison.
 
I love my IH... no gas for me, so it's the best option by some distance !
 

Reply to Replacing ceramic hob for induction - basic questions in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock