Discuss Replacing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Fitzy

-
Arms
Reaction score
251
Tomorrow I’m changing my consumer unit in preparation for my NICEIC assessment on 13th November and have a few queries.

Firstly, current cu only has 4 circuits sockets up & down and lights up & down, so hopefully a pretty straight forward swap.

I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.

Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?
 
I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.

If they have isolators, turn them off and run the full suite of tests (L-N, L-E and N-E). If they don't have isolators join L+N at the board and test L+N to E. This is acceptable when making alterations to existing installations. You just put a LIM in the live-live column for IR.

Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?

Can you access the loft? If so, do the tests from above. It's nice to verify CPC continuity through out, so at the very minimum I would check R2 at each location using a wander lead.
 
If they have isolators, turn them off and run the full suite of tests (L-N, L-E and N-E). If they don't have isolators join L+N at the board and test L+N to E. This is acceptable when making alterations to existing installations. You just put a LIM in the live-live column for IR.

Can you access the loft? If so, do the tests from above. It's nice to verify CPC continuity through out, so at the very minimum I would check R2 at each location using a wander lead.

Unfortunately neither appliance has an isolator, but thanks for the L+N to E tip.

I have access to the loft, but not boarded out, so will have to be extra careful up there.
 
if you only have 4 circuits, i'd fit a BG 6 way RCBO board with 4 RCBOs .get gear from TLC the BG compact RCBOs are ony £15.60 inc. vat each.

I’ve already bought an MK 12 module board, which leaves 4 modules for future additions.
 
A couple of anomilies here
1. IMO its not your responsibility to change the CU. If I was the Landlord I'd be hopping as its unlikely to be part of your initial contract. However, if the landord has given prior permission to upgrade his/her property then fire away. as you will have to use his/her name on the cert.
2. Fixed heating appliances should have local isolation and if connected to a RFC should be by plug and socket or possibly by SFCU/FCU.
 

Reply to Replacing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
593
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
721
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock