Discuss Rewire Problem in the UK Electrical Forum area at ElectriciansForums.net

B

Ben Lewis

Good Morning,

I currently have a Honeywell ST699 heating and hot water programmer which I am looking to replace with the Drayton MiGenie.

However I'm having a few issues with it not working and since the swap over cannot get any hot water or central heating (severely in the dog house at home now!)

Could someone please assist with putting this right as I'm currently stumped.

Thanks in advance

View attachment 35146

View attachment 35147

View attachment 35148

View attachment 35149
 
Good Morning,

I currently have a Honeywell ST699 heating and hot water programmer which I am looking to replace with the Drayton MiGenie.

However I'm having a few issues with it not working and since the swap over cannot get any hot water or central heating (severely in the dog house at home now!)

Could someone please assist with putting this right as I'm currently stumped.

Thanks in advance

View attachment 35146

View attachment 35147

View attachment 35148

View attachment 35149
not enough info. need to know how you've wired it, not just how it should be.
 
On The MiGenie
From Left To Right

Neutral - Blue
Live - Brown
1 - Blue - Hot Water
2 - Blue - Heating
3 - Brown - Hot Water
4 - Brown - Heating

I wasn't sure if I need a link between terminals live, 1&3

Everything was left the same except for the programmer only
 
Hi Ben you are showing the drawing for a W-plan. A W-plan is normally hot-water priority and not typical for a normal house. A W-plan is generally used in places that have lots of hot-water requirements so are you sure its a W-plan?
 
Hi Ben you are showing the drawing for a W-plan. A W-plan is normally hot-water priority and not typical for a normal house. A W-plan is generally used in places that have lots of hot-water requirements so are you sure its a W-plan?

Hi, appreciate your reply being honest I don't know but when reading the manual it said the Honeywell programmer of wired with a link between live, 5 & 8 then it's a W-Plan.

Ive copied the wiring apart from any links from live so I'm not sure if this is what's stopping it all working as I manually applied a live and still nothing happened, I've also linked out the old thermostat and tested that's ok
 
I'm seriously not interested in talking to you so please be kind enough to mind your own business.
This is a forum where people ask questions or advice for free and 99% of the time solve any queries again for FREE. If everyone charged for advice and resolutions then forums wouldn't exist would they.

Actually the main point of the forum is for active sparks to help fellow sparks.....
 
Hi, appreciate your reply being honest I don't know but when reading the manual it said the Honeywell programmer of wired with a link between live, 5 & 8 then it's a W-Plan.

Ive copied the wiring apart from any links from live so I'm not sure if this is what's stopping it all working as I manually applied a live and still nothing happened, I've also linked out the old thermostat and tested that's ok

Can you post a pic of the new programmer wiring?
 
Actually the main point of the forum is for active sparks to help fellow sparks.....

Sorry but the forum is open to all people of all backgrounds, the forums is here to help with the best advice for any member even if that member is a trainee, DIY or seasoned electrician or even just a member of the public asking a related question, it is not an exclusive club.
We expect our members to respond in a polite and helpful manner even if the advice that they give is that they should call in a competent person, what we don't want to see is new or old members been subject to trolling comments as you have done in this thread so be helpful and constructive with your comments or dont bother posting at all, the manner in which the op has responded to you should give you an idea that your input was not appreciated and yes I understand sometimes we get a certain kind of attitude from those asking advice especially when they dont like what they hear but on this occasion the OP hasn't come across like that IMHO and has just reacted to the manner of your posting so please can we show a little more respect.
 
Last edited:
That was not a neutral, it was a switched line coloured blue! I agree it is unlikely to be W-plan. To completely clarify, it would be necessary to understand what type of motorised valve(s) you have and how they are wired. Nonetheless, if you are 100% confident about which wire came from which terminal in the old unit, it is possible simply to transfer them to the correct terminals in the new. The difference between the two is that the common contact of the CH and HW relays is internally connected to Line in the MiGenie, whereas there were separate terminals (5 & 8) in the Honeywell that had to be linked with wires in the terminals. And of course the terminal numbers are different, they map as follows:
Honeywell (H) -> MiGenie (M)
H3 -> M4
H4 -> M2
H5 n/a
H6 -> M3
H7 -> M1
H8 n/a
If you are not sure which came from where, then you have a much bigger challenge as they will have to be traced out electrically.
 
That was not a neutral, it was a switched line coloured blue! I agree it is unlikely to be W-plan. To completely clarify, it would be necessary to understand what type of motorised valve(s) you have and how they are wired. Nonetheless, if you are 100% confident about which wire came from which terminal in the old unit, it is possible simply to transfer them to the correct terminals in the new. The difference between the two is that the common contact of the CH and HW relays is internally connected to Line in the MiGenie, whereas there were separate terminals (5 & 8) in the Honeywell that had to be linked with wires in the terminals. And of course the terminal numbers are different, they map as follows:
Honeywell (H) -> MiGenie (M)
H3 -> M4
H4 -> M2
H5 n/a
H6 -> M3
H7 -> M1
H8 n/a
If you are not sure which came from where, then you have a much bigger challenge as they will have to be traced out electrically.

Thank you very much, I do however have nothing wired in H4 so can't put it in M2 unless you meant I need to link live in to M2 ?
 
If there was no wire in H4 (CH off) then that strongly suggests that the system is a conventional Y-Plan with a mid-position 3-port valve. Correspondingly, there should be no wire in M2. If that blue was just floating about before, it should be made electrically safe as the situation at its other end isn't known.
 

Reply to Rewire Problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
Replies
5
Views
1K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
630
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock