IMO, he could be correct, wooden back boxes is a no no, in the sense if it needed rewiring they would need to be changed, is it red black pvc or VIR.? More info is needed regarding his test, could be low IR.
Yes sir the red and black wire are pvc and very good condition
 
Yes sir the red and black wire are pvc and very good condition
How do you know that they're in good condition? Looking at them inside the dB or at a socket or switch tells you nothing I'm afraid. To know they are in good condition you need to put 500v through them and see what the meter tells you.
 
Also, you would need to know if there is a CPC serving the length of the ring final circuit, which as there's no earth conductor and wooden boxes I would highly doubt it. Again though, this needs to be ascertained through the correct test procedures.
 
Also, you would need to know if there is a CPC serving the length of the ring final circuit, which as there's no earth conductor and wooden boxes I would highly doubt it. Again though, this needs to be ascertained through the correct test procedures.

It's in steel conduit, therefore there must be a cpc at every point already
 
Has anyone ever seen wooden back boxes??? I have seen plinths/pattress but never sunken box. I suspect this is metal conduit with singles drawn through. If so I may be possible to draw an earth through and change the boxes. A picture would soon scotch that conjecture.

Steel conduit is a cpc so why would you add another one inside it?
 
Steel conduit is a cpc so why would you add another one inside it?
I agree wooden boxes is a bit suspect, but saying that stranger things have been found, if it is indeen serviced by wooden boxes the conduit could not be used as the cpc as it wouldn't be continuous. But as others have inquired a picture and proof of the wooden box statement would put the debate to rest.
 
I agree wooden boxes is a bit suspect, but saying that stranger things have been found, if it is indeen serviced by wooden boxes the conduit could not be used as the cpc as it wouldn't be continuous. But as others have inquired a picture and proof of the wooden box statement would put the debate to rest.

The conduit can still be used as the CPC as long a suitable flylead is connected. There were, and still are suitable conduit fittings for connecting a fly lead to a conduit.

I realise they weren't available in the past but these days I use the piranha nuts on the end of steel conduit if I'm running it in to an insulated enclosure .
 

Reply to rewiring in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock