Discuss Ring tripping rcd when connected in the UK Electrical Forum area at ElectriciansForums.net

Does it trip the RCD when you power up the circuit or is it just intermittently?

When you're carrying out the IR test, does your MFT simply run the test and stop or is it like a Megger where you hold the button down and it keeps applying the test voltage and providing readings? I would run a longer test and look for sudden drops in the IR reading. If you get them it can sometimes indicate you have a pinhole in the insulation that won't always show up on a quick test. In which case, investigate any of the accessories you might have worked on or the whole lot if this is a new fault.
 
The Opening post isn't clear.
How are you carrying out IR tests ?

It is possible for a circuit to pass an insulation resistance test when testing between its own conductors, if its isolated from everything else. ( E and N removed from DB)

Something like a screw just piecing through the insulation and touching the live conductor whilst also touching a copper pipe would show the same results.

You need to be more specific.
 
The Opening post isn't clear.
How are you carrying out IR tests ?

It is possible for a circuit to pass an insulation resistance test when testing between its own conductors, if its isolated from everything else. ( E and N removed from DB)

Something like a screw just piecing through the insulation and touching the live conductor whilst also touching a copper pipe would show the same results.

You need to be more specific.

A very good point made.

When conducting IR tests, the cpc should ALWAYS be connected to the earth bar in the CU along with ALL the other CPCs
 

Reply to Ring tripping rcd when connected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
404
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
829
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock