Search the forum,

Discuss rings within rings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

adamh

I tested a job last week and ive been typing up a quote this morning and I cant find a regulation as to why you cant have a ring within a ring or a figure of 8 so to speak.. maybe im half asleep but ive checked the BGB and all i can find is appendix 15 which refers to reg 433.1.103

none of the above makes any reference to rings within rings but im happy I can explain that the circuit cannot be tested properly ensuring continuity of all conductors and therefore the OCPD can not safely be left at 32A. I can not successfully test for spurs or unfused spurs from spurs etc. And on top of that the floor area covered is a couple of hundred square meters so there is a potential voltage drop which i also cannot verify and to boot it has an IR reading of 0.18Mohms


Anyone willing to point me in the right direction? The only place i haven't checked is GN3 but its not to hand this morning. Thanks Adam
 
It's not a 'standard circuit' and would be difficult to test, as it's not a ring or a radial. If it were me I'd try to put it right.
 
Could it be a case of a link across the ring rather than and ring within a ring? That said with an IR of 0.18 something should be done!
 
yes i agree i am quoting to rewire the socket outlet circuits to this part of the house which will end up being an upstairs , downstairs and kitchen RFC. It's a large house and this circuit is massively overloaded and I believe this is the possible cause for the low IR reading even as you start to split it the reading are all very low <2Mohms . I was just going to quote reg nos in my quote and hit a brick wall with the above...
 
yes i agree i am quoting to rewire the socket outlet circuits to this part of the house which will end up being an upstairs , downstairs and kitchen RFC. It's a large house and this circuit is massively overloaded and I believe this is the possible cause for the low IR reading even as you start to split it the reading are all very low <2Mohms . I was just going to quote reg nos in my quote and hit a brick wall with the above...

The low IR would be a good place to start, and if the property is that large surely the best practice approach to make 2 smaller circuits and split the load should work. As for specific regs, ouch!
 
No its not just 1 link the house is old and its had several alterations over the years from 2 dwellings to 1 its had an extension the kitchen has also been moved i disconnected a cable to the alarm and i still had a live but no neutral so there is definately a joint somewhere there and on top of that with it split in several places i still had continuity at the board and a few socket outlets (all different readings)
 
ive got no doubts that i could find and rectify all these faults but with the time and expense of it all it wouldnt be worth it as its not fit for purpose anyway..

i was mainly wondering if there was a specific reg i could of quoted? for future use really :)
 

Reply to rings within rings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top