I have a small Pv farm 5KW. Some months ago inverter started to measure low Riso<1MΩhm (0.8). I tried to test each string alone and with one the inverter read good Riso and started normally. The other had very low Riso. I tried to check the two pv strings but both have same Voc 340Volts. So I think the ground fault may be in DC cable of the second string until inverter. How can I check it with the multimeter? In which way can I check the DC cable (~10m length)? In Ωhm position in multimeter which value should I see and how should I connect with the probes? With ground to one side or not?
 
Last edited:
You'll need to do an IR test on the string. More than likely a failing MC4.
Please could you explain more the procedure?
I tested the Voc of two strings in the roof and they have the same Voc.
So afterwards should I check V between ground and + to see the remaining voltage to find the faulty panel/MC4? And the same procedure down to inverter to see if the cable has any issue?
Thank you very much for your help.
 

Reply to Riso fault Power-One Aurora in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all. Long story short - my Aurora P-One developed the common E031 fault. I carried out the repair myself (ex electronics teacher), replacing...
Replies
0
Views
1K
Hi again. Following my recent zero-Riso issue (unresolved) and also because my system has, in any case, been prone for a good while to the odd...
Replies
10
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock