clip a meter ( on ohms setting) to the terminals. should read zero ( or close to). warm up the sensor end with a lighter. when warm, the stat. should switch and the meter read open circuit.
 
thanks telectrix. why is that? what electrical law is applying to this? It looks like just a metal wire to the earth of the thermostat. (half sleeved, even its not completely isolated) Or this is not a wire maybe some tiny tube etc? Just curious...
 
it's not electrically operated. it's fluid mechanics.the sensor is at the end of a capillary tube full of a liquid. when heated this expands and operates the switch.
 

Reply to Room Sensing Stat in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K
At our church, one of the things I've done is sort out the heating wiring (as best I can for now). The schematic is as shown below. The theory...
Replies
2
Views
2K
Hello, Been remodelling my sitting room and have moved my dimplex duo heat 300n storage heater. This has not been switched on since the end of...
Replies
27
Views
6K
I have just bought a 1 bedroom flat in Cambridge. It's all electric, gas is not an option for me - no gas to building at all. The flat comes with...
Replies
10
Views
2K
N
Hello, I recently bought a 1960s-built house. It had an electric storage heater in it that I wanted to remove. A notice on the heater said to...
Replies
13
Views
19K
Eskimo
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top