Hi, As daft as it seems I have never installed a rotary isolation switch in my life. I've wired for an AHSP whereby 2 x 1 circuits are required, one of which was wired in 10.0mm. AHSP installers require 2 x isolator switches indoors by control equipment. They insist on isolator switches indoors so that they can lock off if working on the AHSP itself. Question is, what make / type >1 Phase surface isolator switch capable of terminating 10mm cable be suitable? I only require it to be 32amp, but would it be better to use a larger amp switch in order to terminate? Thanks
 
you can use a 100A isolator if you want. as long as it's rating is above the actual current, it's not an OCPD, is it?
 
you can use a 100A isolator if you want. as long as it's rating is above the actual current, it's not an OCPD, is it?

No , purely for isolation purposes only. i did the customer when going into the electrical wholesalers to get 2 x 50 amp 1 phase surface rotary switches. They said didn't do 50 amp. Also they wanted to know if 40A or 60A would be OK and if 3 or 4 pole? Do they not do just a 2 pole?
 
use 60A 3 or 4 pole isolators. you don't need to use all 3/4 poles.
 
a 32 amp rotary isolator will be fine, for the ASHP unit. can i ask what ashp isit?
sorry, I don't know the type AHSP. when first fixing a 10mm and a 6mm were required, but now 2 x 6mm would of been OK. apparently newer model doesn't require so much power. I just want to make sure that i can terminate 10mm cables into a switch. My thinking is go larger than 32A.
 
so you should. no point in running an isolator at it's max.
 
They stock whats most popular these days, use the poles you need the rest wont eat or drink anything.
Get the biggest size wise thats acceptable especially if wiring swa cus they can be fiddly little buggers, especially 3p+N&E in larger cable sizes.
 
Just buy the first decent brand one you come across. You would be wise to go for a 63A one to make it easier to terminate, as mentioned they can be fiddly. Most of them have knockouts if not just do what everyone else does and use a hole saw!
 

Reply to Rotary switches. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm installing a temporary supply to a modular kitchen and need to bring over a new 3PN supply for a new temp consumer unit located...
Replies
3
Views
948
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi, I am looking to convert a 2 way light into just control by single switch. I have searched and looked for similar questions here, and found a...
Replies
4
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock