Just completed 15 new builds and on 3 properties the main bonding was run through the pvc sleeve which the gas pipe runs through the caverty wall to the meter outside.
Have now been told that they may not connect the gas meter to those properties unless the bonding is re-routed.
Cannot find any reg thats states you cant run the bonding this way only found this one:
BS6891-2005
8.16.2 Separation of installation pipework from other services
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows: a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
Sates distribution cables nothing about bonds. Any one shed any light on this please
Have now been told that they may not connect the gas meter to those properties unless the bonding is re-routed.
Cannot find any reg thats states you cant run the bonding this way only found this one:
BS6891-2005
8.16.2 Separation of installation pipework from other services
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows: a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
Sates distribution cables nothing about bonds. Any one shed any light on this please