Discuss Running SWA underground in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

18" deep, surround with sand, warning tape at 12" deep, cable suitable considering load and volt drop, better in ducting if possible.
 
was thinking of worst scenario, without details of the exact circumstances. obviously, in certain situations, the depth can be less.
 
Cable route is under a footpath and garden, No heavy use going on above... I was just going to lay the cable about 10-15 inches deep and then lay electrical cable tape above?
 
Cable route is under a footpath and garden, No heavy use going on above... I was just going to lay the cable about 10-15 inches deep and then lay electrical cable tape above?
N

under garden.how deep is a spade thrust? i would go with at least 15" with tape at 10" ( thereabouts.). make sure cable is bedded on sand with sand on top, at least 4" top and bottom. you don't want nasty sharp stones piercing the sheath, do you?
 
Have you ever hit a cable that some lazy sod has not burried deep enough, because I have..
It was in a garden, and I hit it with a fork, fortunatly I knew what I had hit, but someone else might not have been so lucky.
Oh and the lazy sod was the MEB, and they wanted to charge me for the repair...
It just so happened that my brother worked for the SEB, and he told me what I should do about it.
It does not matter where it is, just bury the thing deep enough...
 
Last edited by a moderator:
can't measure in these damned french metric rubbish units. give me feet and inches every time.
 

Reply to Running SWA underground in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

190m run SWA underground, supplied from 3p+N 240mm sub main, each cabin total demand is 80A, worked out 35mm but volt drop is about 8%, would this...
Replies
9
Views
686
Afternoon all. Was wondering, when cables are run underground using mole/tunneling methods, how do people get around the requirement to mark...
Replies
3
Views
381
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
763
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
894
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock