S plan system with 2x under floor heating zones

Discuss S plan system with 2x under floor heating zones in the Central Heating Systems area at ElectriciansForums.net

E

egginyourface

Good evening all,

I'm first fixing property and customer is having splan system with one rad heating zone, hot water and an additional 2x under floor heating zones.

I've taken a thermostat to 3 different zones. What I'm not sure of is how many cores will I need at the programmer?

The under floor heating system is speed fit. I'm bringing someone else to connect it but would like to try get my head round this too

thanks
 
Thanks for replies.


ive run 3core and earth to each under floor heating room stat. Will I need a 4 way programmer to control each zone? I.e DHW/CH/ufh zone 1/ufh zone2.
the plumber has only supplied me with programmer with zone for DHW and CH ?


Thanks
 
Thanks again.

I only have three core and earth at each programable room stat. Looking at the diagram it looks like I don't need a programmer. Am I right?

The zone valve connects into the ufh box of tricks
 
I understand how splan system work. And have no trouble connecting them. Just don't get it when additional zone or zones added to the system for underfloor heating. I'm going to pay someone to connect it for me and will get a better understanding of it.
 
Ok, easy peasy. Keep the normal CH and HW seperate from the UFH, programmer, room stat and cylinder stat as normal, then your UFH will have it's own controls. Three core and earth from the UFH controls to each programmable room stat, the pump and zone valve as well as the actuators will wire into these controls. You'll need a T+E from the UFH controls and from the wiring center to the boiler for your switched line conductors. If the controls for the central heating system are local to the boiler then take a feed for the boiler, UFH controls and wiring center for the normal heating controls from one spur nearby. If controls are not local to boiler, you'll need relays at the boiler so your boiler can have it's own feed. The UFH controls should have labelled terminals so are pretty straight forward for anyone to wire.
 
The thin I don't understand is how will the programmer control the two underfloor heating zones if there is only one zone valve for the underfloor heating manifold? Does the electronics int the ufh box do this?
 
The manifold will have seperate actuators for each UFH zone, these along with the UFH pump and zone valve are controlled by the UFH control system.
 
Hello again everyone

The system has now been connected and working. Used the 2 channel programmer for ch and dhw and 2 programmable thermostats for the ufh.

There's one thing I don't understand, is it ok that the hot water and ch heating pump runs when the ufh heating is on only?

The ufh has its own pump

thansk
 
Then you shouldn't have a problem however I stand by what I say, you have missed out a couple of relays at the boiler connection to prevent both pumps firing up at the same time. There is the potential for the manifold pump to fire up when the HW/CH pump fires up depending on what control system is in place and the manifold almost certainly won't have a bypass valve.
 

Reply to S plan system with 2x under floor heating zones in the Central Heating Systems area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock