mak

-
Reaction score
10
What's the difference between the two, one isolates N the other does not, got me confused when I was testing continuity between E-N, then I realized N was not isolated.
 
There will be occasions where it is not desirable to break the neutral conductor along with the 3 line phases as doing so will present a more dangerous situation.

Which situations are those?

How does breaking the neutral conductor along with the 3 phases present a more dangerous situation?
[automerge]1597330581[/automerge]
Yes I'm trying to ask exactly that.

Ok

The regulations dont require isolators to break the neutral conductor if it is reliably and permanently connected to earth, so in practice you normally don't need to break the neutral where you have a TN supply.
 
The only issue I can see is if on a linked switch, the neutral were to break slightly before the phases, this can lead to 400v across a single phase load on the circuit for a short period of time.
 

Reply to Schneider board main switch TP-N and 4-pole in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
480
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
736
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
389
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
811
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
273

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock