leebut

-
Reaction score
63
Hello Guys


I'm going to put my Tin hat on and close the curtains so the Regs police can't arrest me for asking this question again, I can only find old threads pre 18th edition so please advise me if I'm missing something


I've just been watching a guy on Youtube doing a board change who's said that to comply with the 18th edition of the Wiring Regulations you must seal ALL entry holes into a consumer unit regardless of them coming through the bottom, top, sides or rear entry with a suitable intumescent mastic to stop the spread of fire into the fabrication of the building!!!


I personally am NOT aware that anything changed in the 18th Edition to say all entry points have to be fire sealed I've been looking online tonight and can only find write ups from "Wiring Matters"

Stating


Sealing of wiring entries
It is important for the installer to seal all openings into the enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables - see Figure 6. The intent of the sealing is to ensure that, as far as is reasonably practicable, any fire is contained within the enclosure or cabinet and the escape of flames to the surroundings of the cabinet or enclosure or into conduits trunking or ducting is minimised, as intended by Regulation 421.1.201.
Good workmanship and proper materials must be used, and account must be taken of the manufacturer’s relevant instructions, if any.


Regulation 421.1.201 Does not mention sealing any apertures in a consumer unit with, grommets, glands or sealant and does not mention that the Metal clad board cannot be fitted to a timber backboard. So why is the IET saying we are to be sealing the holes , personally I've been installing all my boards with cables entering from behind and mounting my boards on the existing wooden backboards using a length of stick on trunking as a framework around the consumer unit.


Am I wrong???
 
Just fill the entire board with expanding foam and then gun round the outer edges with an entire tube of fire proof sealant then smooth over with a builders trowel
 
Last edited:
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.
 
The world has gone absolutely crazy imo

We are worrying out bloody fire proof foam when there are still 900,000 death trap tumble driers in people homes And miles And miles of flammable cladding still stuck to the outsides of high rises
 
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.
The plastic rawlplug was brought up at my last assessment, there’s no concern over them as the wall they’re in will support the clips or consumer unit.

This idea of sealing up all the opening with intumescent sealant seems another cash generator to subsidise the cost of changing to metal consumer units
 
Sealing the entries just makes it awkward for the next person adding or altering circuits.
We are supposed to make allowance for future additions when installing DBs, leave spare ways etc, so stuffing the entries full sticky goo seems counterintuitive.
 
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.

If you will the CU up with water then they never catch fire..... Job done...
 
New posts
Status
Not open for further replies.

Reply to Sealing a consumer unit entry points?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
847
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
726
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock