I've come across a fault at work. Fuse keeps blowing when they put it in. I haven't tested for a while, and so am pretty sure I'm missing some basic steps with the fault finding process.
Small room. 1 emergency fluorescent light fitting, 1 bulkhead emergency fitting.
Fluorescent is plugged into a click on the ceiling. Live and Neutral have been wired from this click.
Dead shot L-E.
Unplugged click. d/c bulkhead. Fault clear.
IR test on disconnected cables at bulkhead - >999.
As soon as I connect either fitting, dead short L-E.
What am I missing?!?!
I'm ready for all the abuse.... Come at me... ;)
 
It would point to incorrectly wired click unit IE Live is in the earth terminal etc or the click is internally faulty and the physical action of plugging into it creates the fault... this is going only on the info' you provided, if you have missed any tests or have not been forthwith with all the information then we may be going down the wrong path with my suggestion.
 
I've come across a fault at work. Fuse keeps blowing when they put it in. I haven't tested for a while, and so am pretty sure I'm missing some basic steps with the fault finding process.
Small room. 1 emergency fluorescent light fitting, 1 bulkhead emergency fitting.
Fluorescent is plugged into a click on the ceiling. Live and Neutral have been wired from this click.
Dead shot L-E.
Unplugged click. d/c bulkhead. Fault clear.
IR test on disconnected cables at bulkhead - >999.
As soon as I connect either fitting, dead short L-E.
What am I missing?!?!
I'm ready for all the abuse.... Come at me... ;)
Been doing the bang test a few times then? sounds as though the EM fittings have developed a fault possibly by subjecting them to being re-energised under faut conditions, maybe? Is this a new installation? if yes could be you have the klick plugs wired up wrong.
 
Existing installation. I haven't put the fuse back in personally, but that's not to say somebody hasn't tried before me. When I d/c the L&N that goes from the click to the bulkhead the fault cleared. It all points towards the bulkhead. Funny, because they I had a carbon copy of this fault a few weeks back, and the only way the fault cleared was when I d/c the neutral going from an existing fitting to a new bulkhead. They've basically borrowed neutrals from existing fittings and what not to get these bulkhead light fittings on. All seems a bit heath robinson to me.
 

Reply to Short Circuit When Emergency Lights Are Connected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
395
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
608
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock