Yes they only use a few amps, it is just a pump.so do electrically pumped showers generally use less power than a electrically heated shower?
bloody southerners with posy showers indoors. no wonder you're all soft. :44:
Is it on a 32A ring?
7.2kw is about 31A. They must have very little else plugged in at the time the showers running.
Having said that, cables and protective devices can cope with much higher ratings than the max listed. How longs an average shower? 6-8mins??
You need to stress to the client, that the shower circuit needs to be wired in the correct size cable and own radial,before any CU change, either he agrees to disconnecting the shower if no remedial allowed, otherwise walk away.
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.so do electrically pumped showers generally use less power than a electrically heated shower?
He is not the op.?With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.
There are some pumped and electrically heated showers, but they are, I believe, primarily manufactured for low water pressure supplies. Mira, for example produce some.so do electrically pumped showers generally use less power than a electrically heated shower?
. How longs an average shower? 6-8mins??
with respect you should have gone to spec savers ��