  1. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    I was called into a property where I was told that the shower fuse had blown. On investigation it turned out that a 9.8 KW shower was connected with 10mm T+E but only as far as the nearest fused spur on the upstairs ring main. They'd used a 45A cooker switch to terminate the 10mm then switched to 2.5 to connect into the supply side of the fused spur (which is powering a kind of sit down jacuzzi and seems to be correctly installed). They'd even done it in the old colours!

    Apparently this work was done last August - I've taken photos - the 2.5 in the old colours was melted and fused together - it blew the RCD at the consumer unit and the tenants just haven't touched the shower since it started smoking.

    1) What chance is there that the shower unit is still functional - should I tell her that she needs that swapping and will need a plumber?

    2) What recourse does she have against the shower installers?
     
  2. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    IMHO you should provide an estimate to install the electrics properly and leave the rest to the homeowner.
     
    • Like Like x 2
  3. tonycoysh
    Offline

    tonycoysh Guest

    Sorry this is of no help to you but.......

    You have to laugh or you'd cry!

    Surely you'd be best sorting the wiring out and check the shower and advise her from there? The wiring needs sorting anyway so it's not like you're wasting your time.

    As for recourse maybe she would be best going to citizen's advice or something armed with pictures and see where that gets her first? Or contacting the company?
     
  4. Dave 85
    Offline

    Dave 85 Guest

    Thats class, just class.
     
  5. Dan the spark
    Offline

    Dan the spark Electrician's Arms

    Location:
    Woodley, reading
    I'd do the lot if I were you mate, showers are nice and easy to swap over, nice little profit
     
  6. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    any notification for this shower? ...as in "shower of ****"..lol.....i bet not....given the old colours...lol.........
     
  7. giles-stone
    Offline

    giles-stone Guest

    I thought I'd done a good job n all......
     
  8. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    well we all like to think that we`v done a "good job"...lol......done a good turn more like....as in..quids=arse pocket..lol....
     
  9. DNS1
    Offline

    DNS1 Trusted Advisor

    Shower unit itself should be fine shouldn't it? Wouldn't it have just draw it's normal current until the insulation melted and the RCD/MCB tripped?
     
  10. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    I think the unit should be fine - obviously I'll open it up to see if there's internal damage but was hoping to draw on other's experience as I don't want to be doing a good wiring job on a damaged shower.

    Btw - the original job was apparently done by a "friend of a friend handyman"
     
  11. cook1e
    Offline

    cook1e Regular EF Member

    I would be equally concerned with the rest of the 2.5 mm circuit, the heat build up in the cable will possibly have damaged it elsewhere, not just where it became apparrent

    Martin
     
    • Like Like x 1
  12. tony mc
    Offline

    tony mc Electrician's Arms

    I was called into a property where I was told that the shower fuse had blown. On investigation it turned out that a 9.8 KW shower was connected with 10mm T+E but only as far as the nearest fused spur on the upstairs ring main.

    Some pictures would be good especially re the upstairs ring main fused spur that you mention!
     
  13. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    I too would be concerned about any damage to the supplying "ring". A full test of said circuit must be conducted too IMHO
     
  14. South Spark
    Offline

    South Spark Regular EF Member

    Location:
    South East
    obviously I'm not ticketed for inspections. However it would be pretty straightforward to unplug everything on the upstairs ring and do the full set of tests from the board I suppose.
     
  15. tony mc
    Offline

    tony mc Electrician's Arms

    IMHO I would't worry about tickets etc I would be testing each and every cct that you believe has been affected.

    This is a distress call which has luckily not caused a fire.

    I would be having a good look at the up final ring cct and then performing all the tests having a good look at all the results especially the IR ones just to make sure that the cct is safe to re energise.

    Because of this cowboy install I would stongly recommend that a full periodic inspection be carried out to identify any other problems that might just be hideing!!
     