Discuss Shower Location Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi everybody,

Will anybody be able to help me out with this question? Regarding locations containing a bath or shower, additional protection by RCDs to regulation 415.1.1 of the 17th edition regs states. The use of RCD with a current rating not exceeding 30 mA and an operating time not exceeding 40ms at residual current of 5 1Δn.

Is this telling me that the reading on my meter when testing the RCD covering the circuit is less than 40ms on the x5 setting?

Thanks in advance for any advice on the matter.
 
for most applications, a 30mA RCD must trip in <40mSec. @ 5 x Δn. bathrom is no exceptoin.
 
Hi everybody,

Will anybody be able to help me out with this question? Regarding locations containing a bath or shower, additional protection by RCDs to regulation 415.1.1 of the 17th edition regs states. The use of RCD with a current rating not exceeding 30 mA and an operating time not exceeding 40ms at residual current of 5 1Δn.

Is this telling me that the reading on my meter when testing the RCD covering the circuit is less than 40ms on the x5 setting?

Thanks in advance for any advice on the matter.
 

Attachments

  • RCD TIMES.pdf
    1.1 MB · Views: 23
Seeing's though we're all getting a bit picky - its Xmas, peace on earth, good will to all men & all that :); the OP's title is referenced by reg 701.411.3.3. Which itself refers to reg 415.1.1. using them thereof. The aforementioned reg, refers to low voltage circuits. Just getting in practise for me 18th exam, book reading skills.

'What's it all about Alfie slightly/clueless'?
 

Reply to Shower Location Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

With regards to Regulation 531.3. 3 of BS 7671:2018+A2:2022 Older AC type RCD's are prone to being blinded by dc leakage from other items plugged...
Replies
47
Views
6K
Hello Everyone, We are looking to buy this house but the EICR report have a couple of C2's. Any help advice on these is much appreciated. 5.11...
Replies
4
Views
1K
Hi, I have an Unsatisfactory EICR with the following observations. The flat block was built in 1930 (Art deco) and it was refurbished in 2010 (...
Replies
2
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
433

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock