Badged01
433.3.1 (ii) will apply to an electric shower,if it has fault protection, hence no need for overcurrent protection.
Correct to regulations, if the cable is sized correctly for the overload current then no overload protection is needed.
But what about fault protection without a C/B?. I'll assume there is an RCD for fault current L to E but whats giving fault current protection to the circuit cable for a L to N short/fault? Just need to make sure the DNO fuse is going to 'pop' before the cable melts by running it thro' 'that' calc we are all familiar with.
Practically though, to connect into a way in the CU you will need a C/B so may as well size one up accordingly --- even a 50A one would be acceptable if 'that' equation or manuf data shows the let thro' energy wont melt the conductor before it 'pops'!!