433.3.1 (ii) will apply to an electric shower,if it has fault protection, hence no need for overcurrent protection.

Correct to regulations, if the cable is sized correctly for the overload current then no overload protection is needed.

But what about fault protection without a C/B?. I'll assume there is an RCD for fault current L to E but whats giving fault current protection to the circuit cable for a L to N short/fault? Just need to make sure the DNO fuse is going to 'pop' before the cable melts by running it thro' 'that' calc we are all familiar with.

Practically though, to connect into a way in the CU you will need a C/B so may as well size one up accordingly --- even a 50A one would be acceptable if 'that' equation or manuf data shows the let thro' energy wont melt the conductor before it 'pops'!!
 
The problem with that little gem, is that the supply isn't going to be 230 Volts it, if anything it's going to be in excess of of 240 Volts!!

I don't really understand some of the electricians on here, It's YOU the electrician that make the decision if a cable or whatever is of a suitable size or suitable for purpose, NOT the untrained client. If they are not going to listen to you ....fine, Walk away!! At the end of the day, it's going to be your arse on the line, not the tight as a ducks arse in cramp client!! ...lol!!

So you do all your cal's with measured voltage then eng54? then you know it could be the other way and lower, the guy asked a very vague question and im giving some basic advised, swap it like for like or upgrade the cable. i should after reading your post advised walk away from every job because eng54 will find a way to disagree ....lol!!

That said mate you do know your stuff and make a wicked nay smith.
 
So you do all your cal's with measured voltage then eng54? then you know it could be the other way and lower, the guy asked a very vague question and im giving some basic advised, swap it like for like or upgrade the cable. i should after reading your post advised walk away from every job because eng54 will find a way to disagree ....lol!!

That said mate you do know your stuff and make a wicked nay smith.

I do indeed Ducksy, but then i don't have to contend with phantom make believe voltage bands!!

I don't think you'll ever see lower than 230 volts as you put it in the UK, not unless the installation has some form of voltage optimisation system fitted...

If you have a client that refuses to listen to sound electrical reasoning, that wants you to use an unsafe cable size or accessory that's not up to the job in hand, are you saying that you wouldn't walk away??
 

Reply to shower size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
738
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
630
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock