Unbelievable!!! Last week, bathroom refurb, the shower was removed an 8.5kw mira, it had been supplied from the pullcord in 2.5mm t&e, there was no thermal damage to the cable. The customer says it was there when they moved in, 8 years ago. I cannot believe it has not caught fire & there was no thermal damage!!!
 
Ha, seen this before a couple of times. Lucky the folks didn't like to take really long showers! Saw a shower spurred off a ring once, hmmmm.
 
I'm assuming the 2.5 T+E was installed to method c! Reckon the story would be different if it had been run through insulation!

Certainly shows the safety factors that were used when the 17th edition capacities were calculated! I'd also assume that their supply voltage was at the upper end of the scale...
 
I've come across this before and I've always wondered why they don't get nuisance tripping! and also is a shower wired in 2.5 on a 20amp breaker actually dangerous?
 
I've come across this before and I've always wondered why they don't get nuisance tripping! and also is a shower wired in 2.5 on a 20amp breaker actually dangerous?

Not dangerous assuming the 2.5 is installed in a reasonable way... Can't see the shower working for long though
 
I've come across this before and I've always wondered why they don't get nuisance tripping! and also is a shower wired in 2.5 on a 20amp breaker actually dangerous?

Nope, may trip regularly though


Best I've found is a shower wired on 1.5 flex spured from the ring, luckily the flex melted to protect the 13 amp fuse :lol:
 
hope my mate's hotel is OK. he's got 5 showers all on the ring final. oh, forgot to mention, they're power showers.
 
Unbelievable!!! Last week, bathroom refurb, the shower was removed an 8.5kw mira, it had been supplied from the pullcord in 2.5mm t&e, there was no thermal damage to the cable. The customer says it was there when they moved in, 8 years ago. I cannot believe it has not caught fire & there was no thermal damage!!!

Had this once, melted a hole in the CU fuse carrier. Two previous sparkies couldn't find the problem!
 
I had one recently, called out for a faulty shower.
checked power at iso switch, all ok, 6mm in, 6mm out.
Went to isolate at c/u and found the 40A MCB, but as it was a metel clad wylex I could see the cable leaving the fuse way was a 2.5!
Turns out their mate who 'has all the papers to be an electrician???' fed it from the disused immersion switch in the airing cupboard.
nice.
 
One that sticks in mind was my sister asked me check the wiring in her first house purchase in the 80's (that bad I did a complete rewire) shower was wired in 2 x 2.5 in parallel, problem was 1 neutral and 1 earth were cut off at the sheath, installer only needed the red "important" wire?
 
I have a 9.5kw in mine with a 6mm protected by 32amp breaker.....it's never tripped out and I have long showers.......you will find if you put your clamp on round it it will not draw anywhere near what the rating of it is hence no thermal damage!
 
I have a 9.5kw in mine with a 6mm protected by 32amp breaker.....it's never tripped out and I have long showers.......you will find if you put your clamp on round it it will not draw anywhere near what the rating of it is hence no thermal damage!

It's true. I installed my shower a few years ago, it's a 9.5kw model supplied with 10mm. Put it on a 32amp breaker at the time as it's all I had spare, kept meaning to change it for a 40 but never actually needed to.

Not just the showers that draw less than you think, but MCBs can withstand more and for longer than some folks think!
 

Reply to Shower supplied via 2.5 T&E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I was tracing some electrical cabling last night and noticed a ~6" section of 2.5 T&E cable that appears to have been subject to heat damage and...
Replies
19
Views
2K
Been asked to advise on a rewire. I think on age alone it's advisable but the following points add to the argument. Installation age approx 60...
Replies
15
Views
2K
I was doing a eicr today. Came across a shower 9.5 kW Mira ,which had been installed for at least 8years. its was brutally spurred off the...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock