Discuss Shower tripping sockets rcbo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
8
On call and the socket rcbo is tripping when the shower gets turned on.i have traced the shower cable and it goes from db to switch to shower.there is nothing connected into the sockets it is on a 40 a rcbo the sockets are 32a

The socket rcbo trips but the shower one doesnt.

Any thoughts?
 
Has it ever worked before? If not then I would suspect the neutral for the shower is somehow connected to the sockets RCBO.

Continuity test should show that.
 
On call and the socket rcbo is tripping when the shower gets turned on.i have traced the shower cable and it goes from db to switch to shower.there is nothing connected into the sockets it is on a 40 a rcbo the sockets are 32a

The socket rcbo trips but the shower one doesnt.

Any thoughts?
Any testing done to prove anything???????
 
Could it be a N-E fault on the 32A ring that is set off by the shower current? If so, a load in the 32A ring should cause trip too. Just a thought.
What he said^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
 
There has been a few posts recently about RCBO RCD tripping when circuits not connected to that RCD have been energised!

Richard Burns has put up a diagram explaining how this could happen I will see if I can find it.

Have you tested both circuits fully and checked for any loose conections including the main switch?
 
I swapped the 2 rings round hoping it would trip the downstairs ring ie faulty rcbo but no kept tripping the upstairs.

Wouldnt a ramp test just tell how much of a fault current is lifting the rcbo?still cant figure out why a sepwrate circuit is causing it to trip
 
You are ahead of me ... the ramp test will help to find it if was on a hair trigger. You did that by changing RCBO :)

Can there be any connection between the cables of the ring and the shower somehow? Perhaps an IR check to confirm they are in fact independent?
 
Have you tested the shower itself? Out of interest, what make is the RCBO?

PS have you tested RCBO's with circuits disconnected, to ensure they are functioning correctly ?
 
Last edited:
I would get your earth clamp meter out and see what the leakage is.... you may be getting good IR results with appliances isolated but when they are turned on.....the leaking starts.....
 
The fault must be located on the circuit that the RCBO is protecting i.e. the sockets, because, unless the shower is cross connected into the socket circuit, then the RCBO cannot react to a fault on the shower.
The shower being turned on and tripping the socket RCBO means (some of, >30mA) the shower current is passing through a fault on the socket circuit.
 

Reply to Shower tripping sockets rcbo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Rcbo tripping on 1/2 settings with load connectted but ok when load disconnected all other tests are fine… FI required but any thoughts on this😎
Replies
10
Views
852
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
854
I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock