I have been asked to install a isolator to extend some cables feeding a chiller.

Normally I would just run another multicore swa to the new location but they have had it designed with 240mm armoured single core to the new location. Of which they are not budging on.

But the chiller is outside so what options do I have for retaining ip rating of the enclosure and stopping eddy currents.

I have a few options I have thought of just seeing how others would do it.
 
I have been asked to install a isolator to extend some cables feeding a chiller.

Normally I would just run another multicore swa to the new location but they have had it designed with 240mm armoured single core to the new location. Of which they are not budging on.

But the chiller is outside so what options do I have for retaining ip rating of the enclosure and stopping eddy currents.

I have a few options I have thought of just seeing how others would do it.
would a mf joint be acceptable to extend it?

when i was in derby hospital they have about 4 on tray or in subs that have been extended.

i dont know what size they are but they were thicker than my calfs
 
They want an isolator didn't have one before but gives local isolation which is better than not having any. It's just the termination into the metal box retaining the ip rating im after some more ideas on incase someone had a better idea than mine.
 
They want an isolator didn't have one before but gives local isolation which is better than not having any. It's just the termination into the metal box retaining the ip rating im after some more ideas on incase someone had a better idea than mine.
jigsaw it out and use a non ferous gland plate if you are going to have multiple swa cables glanded into it.

my engineer stepdad just chirped up they use fr4 plastic for the glandplates
 
Last edited:
I have been asked to install a isolator to extend some cables feeding a chiller.

Normally I would just run another multicore swa to the new location but they have had it designed with 240mm armoured single core to the new location. Of which they are not budging on.

But the chiller is outside so what options do I have for retaining ip rating of the enclosure and stopping eddy currents.

I have a few options I have thought of just seeing how others would do it.
Didn't know you could get single core SWA. You'd think there can't be many uses for it.
 
A lot easier to work with four single 240mm2 armoured cables than it is one four core 240mm2.

Darkwood got in there first.

The cutting slots was my first thought with epoxy but sounds a bit rough? Normally I'd make a gland plate but not really enough room to cut the old one out and fabricate something to fit.
 
Last edited by a moderator:
Didn't know you could get single core SWA. You'd think there can't be many uses for it.

Of course you can, it just has aluminium armour instead of steel for obvious reasons.
The use of single core steel SWA is not permitted under 7671.

Confusion comes in due to the two definitions for SWA. It's either steel wire armour or single wire armour.
 
I have been asked to install a isolator to extend some cables feeding a chiller.

Normally I would just run another multicore swa to the new location but they have had it designed with 240mm armoured single core to the new location. Of which they are not budging on.

But the chiller is outside so what options do I have for retaining ip rating of the enclosure and stopping eddy currents.

I have a few options I have thought of just seeing how others would do it.
Check tables 4D3A and 4E3A of BS7671.
Particularly the note about the armour.
 
I've seen/used plastic gland plates with rubber cut to size grommets, for the IP rating and the cable is clamped externally on ladder rack or unistrut and internally in the panel, you can get configurations of upto 6 cables I think,

Only used these in Europe though, on 240mm+ single and smaller multicore cables

I have seen Schneiders version in UK on a few installs
 

Reply to Single Core SWA in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock