all depends what the customer wants you to do. if he wants them leaving as is, then leave them. if there is danger of the flex being damaged, note it on your cert.
 
Customer is a landlord who's wanting a safety cert so can rent property out
all sockets at moment are on metal switch boxes in skittings
all are single unswitched sockets
 
as long as earthing is in order and test results are OK, no problem.
 
What I was going to do but he said had number of sparks round saying must be pulled out and chasing above or surface boxing above
 
It is certainly a good idea to raise sockets up to the recommended levels, but in no way MUST this be done.
If you are doing an inspection then the results are as Tel says.

If he wants to move the sockets up then this is a separate issue and can be done.
 
Iv had that recently client asked if turning some would help It did but with the adaptors for somethings coming out top a couple were left as was
 
I've known customers to be told that it's a fire hazard as the skirting is wood!!!!

No I wasn't me that told them that either!!!!
 
Your doing a cu change not a rewire. Note it, recommend to the client that its best that they are relocated to a higher position so not to put strain on any flex and that's it.
 
I'm sure all this stems from people getting domestic registered from showing a spur in the garage to pass and not actually being on the tools and learning. No good will come of this to the public, we will be viewed as no better than a pikey builder.

Newsome, I hope you put him straight on this.
 

Reply to Skirting sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hi, I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can...
Replies
6
Views
710
Hi there, I am looking for some advice re: putting new sockets and usb sockets in my home. Someone will be rewiring the entire house but I have...
Replies
19
Views
1K
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
583

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock