  1. electronurd
    Offline

    electronurd EF Member

    Location:
    Sheffield
    Hi all,

    I have noticed something very odd in my home. All of the small bulbs keep blowing. When I say small i mean the fridge bulb, the freezer bulb and today the cooker bulb blew, tripping the fuse and this was a brand new bulb fitted only a week ago.

    I was just wondering if anyone knew what could be causing this please?

    Thanks in advance.
     
  2. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    if you think about where lightbulbs are made and shipped from all over the world I'm not surprised .
     
  3. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
    Is it a cheap brand of lamp
     
    • Like Like x 1
  4. electronurd
    Offline

    electronurd EF Member

    Location:
    Sheffield
    Thanks guys but this one is a definite weird one... the bulbs actually shatter and i've never know 3 different bulbs which should last a decent amount of time all blow after just a few days of use.
     
  5. TonyMitchell
    Offline

    TonyMitchell Regular EF Member

    Location:
    Berkshire, UK
    Many cheap lamps are intolerant to overvoltages. If lamps in different appliances on different circuits persist in blowing, first off I would check the voltage. But not just once during the day. A few months ago at home, we were in the low 240's during the day, however by late at night this was up into the mid 250's, over the +/- 10% threshold. The DNO monitored it for a few days, then tapped it down at the transformer.
     
    • Like Like x 2
  6. electronurd
    Offline

    electronurd EF Member

    Location:
    Sheffield
    I have a feeling this is more like it... I do not know however how to test this. Might need to get someone in to have a look.
     
  7. TonyMitchell
    Offline

    TonyMitchell Regular EF Member

    Location:
    Berkshire, UK
    You can buy a cheap 'plug-in' 13a consumer voltage meter, which although it may not be particularly accurate, should be good enough to indicate if you are getting either wide fluctuations (increases at off peak times being the common scenario) or indeed if your supply voltage is too high all the time. Your DNO will sit up and listen as soon as there is reasonable evidence that you're getting over 253v. Or if you have a local, friendly spark, taking a reading is quick & simple.
     
  8. 1Justin
    Offline

    1Justin Electrician's Arms

    Location:
    Surrey
    Business Name:
    Circitas Ltd
    Fridge and freezer (not oven) you can fit LED instead of halogen. They will be much more tolerant of on/off cycles, vibration and voltage fluctuation.
     
    • Like Like x 1
  9. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    Business Name:
    David Haddock Electronic Repairs
    If the glass is shattering ?
    That indicates "cheap quality syndrome"
    The market is full of cheap poor quality lamps.
     
    • Agree Agree x 2
  10. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi E - I've not seen fridge or oven lamps shattered, but that would make me think they did not have the tempered glass that could withstand their environments, rather than suspect the electricity supply. Perhaps try new lamps from a new source?
     
    • Like Like x 1
  11. NDG Elecs
    Offline

    NDG Elecs Electrician's Arms

    Location:
    Tyne and Wear
    To add, a lot of European imports are geared towards 220V I believe. Are you close to an electricity substation perhaps? If so, your incoming voltage could be on the high side. As Justin said above fit LED to the cold appliances, that should help. And try a good brand for the oven (although sometimes I doubt the difference between cheapo and expensive).
     