Hi all,

I have noticed something very odd in my home. All of the small bulbs keep blowing. When I say small i mean the fridge bulb, the freezer bulb and today the cooker bulb blew, tripping the fuse and this was a brand new bulb fitted only a week ago.

I was just wondering if anyone knew what could be causing this please?

Thanks in advance.
 
Thanks guys but this one is a definite weird one... the bulbs actually shatter and i've never know 3 different bulbs which should last a decent amount of time all blow after just a few days of use.
 
Many cheap lamps are intolerant to overvoltages. If lamps in different appliances on different circuits persist in blowing, first off I would check the voltage. But not just once during the day. A few months ago at home, we were in the low 240's during the day, however by late at night this was up into the mid 250's, over the +/- 10% threshold. The DNO monitored it for a few days, then tapped it down at the transformer.
 
You can buy a cheap 'plug-in' 13a consumer voltage meter, which although it may not be particularly accurate, should be good enough to indicate if you are getting either wide fluctuations (increases at off peak times being the common scenario) or indeed if your supply voltage is too high all the time. Your DNO will sit up and listen as soon as there is reasonable evidence that you're getting over 253v. Or if you have a local, friendly spark, taking a reading is quick & simple.
 
Fridge and freezer (not oven) you can fit LED instead of halogen. They will be much more tolerant of on/off cycles, vibration and voltage fluctuation.
 
Hi E - I've not seen fridge or oven lamps shattered, but that would make me think they did not have the tempered glass that could withstand their environments, rather than suspect the electricity supply. Perhaps try new lamps from a new source?
 
To add, a lot of European imports are geared towards 220V I believe. Are you close to an electricity substation perhaps? If so, your incoming voltage could be on the high side. As Justin said above fit LED to the cold appliances, that should help. And try a good brand for the oven (although sometimes I doubt the difference between cheapo and expensive).
 

Reply to Small Bulbs Keep Blowing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi, Our house is 150m away from the street. We installed a 600V step-up/down system to bring electricity to it in order to avoid excessive losses...
Replies
9
Views
871
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock