Not sure about banking and shaming possibly should remove that post. He has fitted a very cheap basic con unit so as said 400 to do the job properly and would take a full day if you have a full test and all paperwork filled out. Why does he keep starting at 6pm? Would be good to see inside the board. Wonder if gas and water are even bonded in 10mm seeing as we are assuming that overheard line has been converted into a pme system????
 
This earth is connected to the water pipe outside the cupboard and another on the pipe inside near the CU

IMG_20170615_111456843.jpg
 
I've just been looking at the before and after pictures
BEFORE

AFTER


Once upon a time, this was a TT installation.
It would seem that he has removed the old VoELCB and done a "DIY" conversion of the supply to TNC-S. I thought that this could only be done by the DNO (electrical supplier), and not your general jobbing electrician.
but is it TNC-S. who knows if there's a N-E link in the head, and who knows if the supply is PME
 
but is it TNC-S. who knows if there's a N-E link in the head, and who knows if the supply is PME

He'll have had the main fuse out to fit the DP block where the old voltage trip once lived, maybe even put in a link himself ! Without seeing inside the board this job is rough as, why leave the main earth that long, no effort made to tidy or secure the tails and you can see the inner insulation on both old and new tails at the new block, shoddy !
 
for the CU change including certificate and fixing minor problems no more than £400 on my shift.

edit. just seen you rlas post. put the freezer on an extension lead to a working socket.

£400 for doing it out of normal hours? I'd be wanting a lot more for giving up an evening to do it.
 

Reply to Smoke coming from electric meter/fuse box area in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
626
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K
Hi all, I am an experienced DIY electrician and I just wanted to ask a quick question about something since I am new to this forum, if it hasn’t...
Replies
11
Views
1K
Hi everyone! Im not an electrician but just a guy looking for a possible answer before I call my electricity supplier. Every month without fail...
Replies
11
Views
2K
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock