Your last comment is not correct, I have taken the comments from the latest edition of BS7671 that was only bought from the IET about a month ago and the definition does not appear to have changed.
The issue with the lighting circuit should really be determined by the size of the bathroom because if the ceiling height is less than 2.25m or the bottom of the luminaire is below 2.25m then Reg 701.411.3.3 must be adhered to that requires the lighting circuit to be RCD protected in accordance with Reg 415.1 which requires the RCD to have a 30mA rating.
Now as BS5839-6 clearly indicates that smoke/heat detectors should not be on an RCD rated at 30mA such a circuit should not be used.
The problem this introduces is that many domestic bathrooms in the UK do not have ceilings that allow for the bottom of the lights to be greater than 2.25m (7ft 4") from the floor. Clearly many do, but you would need to be sure first to ensure full compliance with both sets of regulations. My personal thought, and clearly others will see it as they wish and that is fine, that to ensure full compliance regardless if the snoke/heats are on their own circuit then you are on safe ground.
Just wondering Outspoken:
Why are you suddenly such an expert on domestics when by your own admittance you hate 'them' and don't do 'them'?
Why did you only buy the BGB last month when the Regs changed last year? I presume the update doesn't apply to you?
I don't understand why you are waffling on about bathrooms and smokes? What relevance is this to the discussion? How many smokes do you see in the bathrooms of average houses? I guess you must live in a mansion, being super-paid as an industrial spark