Looking at rewiring a kitchen for a customer. In a previous renovation they had french doors installed which left a socket almost on the corner of the opening Now that I am looking to fully revamp the kitchen including a new CU is there a reg that says how close to an opening a socket can be ? :confused:
 
No specific Reg as such, but could fall foul of external influenceses section of regs ,if you consider it could be knocked when going in and out of the door or if it is likely to be splashed by rainwater .also the flex of-Any appliance plugged into it may also cause a tripping hazard at the doorway-your descision really Sanke
 
Last edited by a moderator:
Hi sparklad
Not overly happy with positioning as when doors open etc the socket could get wet & of course there is the tendency to use it to power lawnmower etc
Need to take a spur feed to island unit so wil probably use this, thus getting rid of the socket :)
 
Sounds like a good solution--by the way why is it a problem if someone was to use it for the lawnmower ? it is RCD protected isnt it ? or at least it will be when you fit the new C.U wont it ?-- are you referring to the tripping hazard ?
 
i don't think he means the rcd tripping more like trailing the lead for the lawnmower if some one walks out the house and trip over the lead they will be seeing the stars
correct me if am wrong sparkylad
 
A cable plugged into a socket by the kitchen door is less of a trip hazard than one plugged in on a penninsular unit within the kitchen for example.
 

Reply to Socket position in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
826
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
720
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
810
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock