The worst one I ever came across was in a training centre for electricians,a single metalclad socket below a DB,connected to this by a coupler and 2 bushes was another single socket,now one was fed off red phase and one off yellow phase,with both sets of feeds going through the first box.I commented on it to one of the instructors who replied "it'll be ok one of us fitted it so we know about the way it's done"
 
why would you need warning signs?? for what?
In the event of simultaneous line to earth faults on appliances using these socket outlets, the metalwork on both would rise to mains voltage until the protective device for each has operated to clear the faults. This is highly unlikely, but is possible. If it did occur, shock voltage when the metalwork of both were to be touched simultaneously would be 400V, not funny.
 
In the event of simultaneous line to earth faults on appliances using these socket outlets, the metalwork on both would rise to mains voltage until the protective device for each has operated to clear the faults. This is highly unlikely, but is possible. If it did occur, shock voltage when the metalwork of both were to be touched simultaneously would be 400V, not funny.

Note, thread is 8 years old.
 
There are times when it might be prudent to attach a sticker.

but to my knowledge, it is not a requirement.
I will of course change my opinion when someone points me towards a relevant reg. number.
 
I think they did away with the need for 400v stickers when they realised anyone fiddling with a lightswitch would have isolated it at the board first, noticed it was a 3 phase board and knew to check.
Because only qualified electricians work on electrics... right??
 
I did a really nice office fit out some time ago. Everything was new, crisp white walls, chrome trim round internal glazing units.
looked great, the real dogs danglers with no expense spared.

all certified, photographed for posterity, invoiced submitted.

2 days later, bearing in mind it was a job I was proud of, director phones me up having a right grumble about my work.
light switches not level, dirty fingerprints and even the warning stickers were on the ---- and looked awfull.

I said something along the lines of that was some of my finest work, and suggested we met on site right now to sort these issues out.

half an hour later we are walking round and he was quite right.
turns out there maintenance guy had been in after me, inspected my work, left prints on the walls and put ghastly warning stickers on the walls by the light switches and along the dado trunking.

boss was fuming, called let’s call him ”bob” to the meeting room.
one of the things that Bob was absolutely adamant about was that it was not to regs and should not be signed off because of the lack of warning stickers.

he really went for it, trying to take strips of my workmanship and understanding of the regulations.
I stayed fairly quiet for most of it, when the boss eventually stopped him and asked me what I was going to do about it I bluntly told him that bob was full of carp.
placed a copy of the wiring regs on the table and challenged Bob to back up anything he had just said by pointing it out in the book.

when he couldn’t do it, the boss thanked me for my time, shook my hand and said he would be in touch.

to my surprise when I got home that evening, still a bit worried about it all, I found the invoice had been paid in full a month before it’s due date.

Bob was no longer working there when I went back for some other work a few months later.
 
I did a really nice office fit out some time ago. Everything was new, crisp white walls, chrome trim round internal glazing units.
looked great, the real dogs danglers with no expense spared.

all certified, photographed for posterity, invoiced submitted.

2 days later, bearing in mind it was a job I was proud of, director phones me up having a right grumble about my work.
light switches not level, dirty fingerprints and even the warning stickers were on the ---- and looked awfull.

I said something along the lines of that was some of my finest work, and suggested we met on site right now to sort these issues out.

half an hour later we are walking round and he was quite right.
turns out there maintenance guy had been in after me, inspected my work, left prints on the walls and put ghastly warning stickers on the walls by the light switches and along the dado trunking.

boss was fuming, called let’s call him ”bob” to the meeting room.
one of the things that Bob was absolutely adamant about was that it was not to regs and should not be signed off because of the lack of warning stickers.

he really went for it, trying to take strips of my workmanship and understanding of the regulations.
I stayed fairly quiet for most of it, when the boss eventually stopped him and asked me what I was going to do about it I bluntly told him that bob was full of carp.
placed a copy of the wiring regs on the table and challenged Bob to back up anything he had just said by pointing it out in the book.

when he couldn’t do it, the boss thanked me for my time, shook my hand and said he would be in touch.

to my surprise when I got home that evening, still a bit worried about it all, I found the invoice had been paid in full a month before it’s due date.

Bob was no longer working there when I went back for some other work a few months later.
Don't be a "Bob"
 
The requirement to put in place a notice where voltages above 230 is present in or between enclosures was removed some time ago in one of the 16th Editions. It is no longer necessary.
...and that's a long time before Dec 2013, when this thread started.
 

Reply to Sockets on different phases in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
477
Hello All done an EICR on a small office around 5 years old someone has added extra socket circuits from new to suit layout. they have added...
Replies
6
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
883
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
578
Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
416

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock