Search the forum,

Discuss Sockets stopped working in the The Welcome Forum area at ElectriciansForums.net

Reaction score
4
Hi there! I am new to this site and was hoping someone can help me as I have a problem with my elecrics and can’t seem to find the issue . 9 plug sockets have stopped working in three rooms but none of the circuit breakers have tripped in the main board. I have checked the wire connections and plug sockets but there doesn’t seem to be any loose wires or indication of damage. Can anyone help?
 
Are all the other circuits working?
It could be that the CB for the sockets has tripped, but the switch has, because of a faulty Circuit breaker remained physically in the on position, try switching it off and then back on again, if this is successful, then sods law says you have a faulty CB, time for an electrician to be called upon, not an expensive job, but well worth doing, if you were closer to my location I would pay you a visit.
 
Last edited:
Yes everything else is working apart from the 9 plugs. It’s strange as it seems other plugs on the same circuit are working

As @Pete999 suggests, they may be on a different circuit.
Switch off the breaker for the sockets and see if the 'working' sockets are still working. That will confirm the sockets are on the same circuit.
 
Are these sockets all in a new room? It could be that someone has added these with a 13A switched fuse at the beginning of the string of sockets. If the total load has exceeded 13A then it may have popped, or someone might have turned it off.
Do you have one of these and have said to yourself "I wonder what that is for".

AA13SCF.JPG
 
i'd make a guess they are all on 1 circuit. are they identified in the consumer unit.and can you post a pic of said consumer unit?
 
To give a indication of what could be checked,knowing the circuit type would be handy,is it a radial or a ring

What circuits do you have listed on your consumer unit and what configuration are the protective devices

Picture of cons unit ?
 
In my experience of inspection and tests, the number of non-continuous conductor faults on RFCs, that remain undetected until the test, is very high. My guess is that there are now two of these faults, at either end of the faulty section.
Have any of the socket fronts been disturbed recently?
 
They could be on a different circuit, have you tried my point post 6?
Ok I’ll try answer all the questions sorry if I miss any I tried point 6 but the 9 plugs are still not working but I do think that they are on the same circuit so may be an issue with the CB. I’ve attach a picture of the cons unit- it states it’s a ring circuit. I think the issue is with the 4th CB to the right (currently switched 0ff) as when it is down or up it does not affect any of the other plugs so I am assuming it is linked to the 9 plugs that are not working. Could I try switching the CBs or should I call an electrician? Thanks again!

6C1CFD2D-4AD0-4344-88D9-1BA8DEB9E33B.jpeg
 
In my experience of inspection and tests, the number of non-continuous conductor faults on RFCs, that remain undetected until the test, is very high. My guess is that there are now two of these faults, at either end of the faulty section.
Have any of the socket fronts been disturbed recently?
Yes I have just bought the place and the sockets are coming away from the wall. I recently plugged something in and now 9 plugs have stopped working.
 
Ok I’ll try answer all the questions sorry if I miss any I tried point 6 but the 9 plugs are still not working but I do think that they are on the same circuit so may be an issue with the CB. I’ve attach a picture of the cons unit- it states it’s a ring circuit. I think the issue is with the 4th CB to the right (currently switched 0ff) as when it is down or up it does not affect any of the other plugs so I am assuming it is linked to the 9 plugs that are not working. Could I try switching the CBs or should I call an electrician? Thanks again!

View attachment 40267
Best get an electrician in to inspect and test the circuit.
 
Ok I’ll try answer all the questions sorry if I miss any I tried point 6 but the 9 plugs are still not working but I do think that they are on the same circuit so may be an issue with the CB. I’ve attach a picture of the cons unit- it states it’s a ring circuit. I think the issue is with the 4th CB to the right (currently switched 0ff) as when it is down or up it does not affect any of the other plugs so I am assuming it is linked to the 9 plugs that are not working. Could I try switching the CBs or should I call an electrician? Thanks again!

View attachment 40267
why is that 16A breaker off? could that be the problem?
 
It’s a 16A MCB, so the circuit probably is a radial. Maybe it simply was overloaded.
@Connan Gibson turn that MCB on and see is anything starts working.

If not, then you’ll need an electrician, unless you are handy with a test meter.
 
Looks like he has already tried the breaker.
Spoon the OP intimated that it "didn't affect any of the other sockets" now to me that indicates he didn't try the sockets that had failed, nor did he say if it tripped when he switched it on, his initial post did not mention any breakers that were off, summat odd going on? Whats your take?
 
Whats your take?

Buggered if I know mate.. It all sounds strange.

I think the issue is with the 4th CB to the right (currently switched 0ff) as when it is down or up it does not affect any of the other plugs so I am assuming it is linked to the 9 plugs that are not working

Hi OP. Just out of curiosity, are you saying that when the 4th breaker if off all the other sockets in the area are working besides the '9 faulty' ones?

Yes everything else is working apart from the 9 plugs. It’s strange as it seems other plugs on the same circuit are working
 
Buggered if I know mate.. It all sounds strange.



Hi OP. Just out of curiosity, are you saying that when the 4th breaker if off all the other sockets in the area are working besides the '9 faulty' ones?
Correct. Must be that the other plugs are on a different circuit then the 9 faulty ones. Will let you know the outcome once the Electrician has had a look. Hopefully its not going to be expensive!
 
how does the 16A breaker feel compared to others?is it sloppy when switched or do you get a distinct click? could be that the breaker has been overloaded over a period of time and just died.
 
The other -or- is more dangerous - half RFC alive , and prone to overload . Do get some-one in soon !
(Has any decorating been done recently ?)
 
Last edited:
It sounds as if you have a 16A radial circuit with nine sockets on it.
This is the circuit breaker you have identified even though it is unlabelled in the consumer unit.
It sounds as if there is either a loose connection that pulled out of a terminal between the circuit breaker and the first socket in the line or that the circuit breaker has failed.
If you were to describe to the electrician that you plugged something in and these specific nine sockets in the lounge and the two bedrooms stopped working but no protective device tripped and that the only circuit breaker that now does not appear to do anything is the unlabelled one then they should be able to resolve the problem fairly easily. If you were to tell them that you have a high integrity MK sentry consumer unit then they should be able to have a circuit breaker available if a replacement were required.
 
Another possibility is that the 16a MCB is just a spare. There is what appears to be an RFC marked as kitchen, and one marked as ring circuit, which in a small house could cover the living room and bedrooms. Perhaps reseetting this one is worth a go?
 

Reply to Sockets stopped working in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
687
Have a single plug socket which has been working fine for years. It is behind a unit so nothing has hit it. I looked at the socket and can seen no...
Replies
13
Views
1K
Hi all, I'm wondering if anyone might be able to help. We have a fused switch that controls 4 LED lights next to a power socket which have both...
Replies
11
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
764
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
511

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock