D

danesol

Order placed tonight - delivery hopefully this week !

I'm going to document the installation and present ongoing results for interested parties as todate no-one seems to have done this

WATCH this space...................
 
Had mine installed by Solar and Electrics Worscester last Friday when my PV system was installed.

I ordered the mk3 2 weeks before the installation and was told it would be with me, the day before it hadnt arrived so I called and spoke to a helpful chap who arrnaged to sent it next day before 10am. I do believe they have some issues in getting the units out the door !

Looked quite straightfoward to install, although Tarum had installed the unit before.

It works very well, so well my water is too hot, limited control on the immersion element. I added a Mangers tank jacket to my foam lagged tank and its still very hot in the morning before any production.

I do have a issue that the lcd display goes blank and can scroll odd letters, reported this and waiting for a replacement unit to be sent out. I hope I was just unfortunate, but Dan from SolarImmersion has been helpful so far.

Would I recommend the Solar Immersion mk3, yes I would, no flicker issues like the Immersun. My only critism is I would like to see how much is being sent to the immersion, ie today 4.5kw.
 
OK, unit arrived, fitted and working away !!

Points so far;

1. Unit is made of a simple Rittal like box with openings top & bottom of unit for cable entries. These have to be removed where required and we used proper electrical glands for fitment.

2. Unit comprises internally of a display unit, a PCB, a large main connector block ( black with connection markings above on the PCB ) and naturally an earth connection bar and connection for earth bonding.

3. Unit is constructed well, but NOT as good looking as say the Solic unit, however I'm after functionality not looks as its hidden out of sight anyway. Its definately a well thought out system with a NO frills attitude, so if you are seeking an excellent "looking presence" with "detailed reporting" you will be disappointed - lol

4. IMO - the main connection block is too thin & flimsy - they could of done using using a stronger more robust connector as while tightening it tended to twist just slightly, large wires were hard to get into the holes, but this is been picky and not really criticising as such.

5. Once switched on and setup with the various options in the menu - it started to work straight away but I have now noticed the display is now dim and you cant see it as brightly as before - haven't worked out how you constantly brighten the screen yet, but will investigate this later !

6. Various instructions in pdf format ( website ) are excellent

7. I'm not going to personally recommend this unit just yet , till I've seen a few weeks results but its looking very promising so far !!

Anyway - thats all now done and I will report back with result findings over the next week or so !!

here's a couple of picture of the actual contents;

CIMG8484.jpg

CIMG8485.jpg


 
Last edited by a moderator:
Typical - order with the above discount code already given BUT get a further discount on postage for the next few days apparently !!!!

""2 Day Special Spring Offer - Use the coupon code SPRING13 at checkout to get 50% off on postage""
 
Im still trying to get my faulty unit swapped, such a shame a great product is marred by poor customer service.

When you say "blank screen" - are you saying the same as I:- Screen goes from bright green characters to very low level LCD just like the old watches, or do you really mean you cant see anything at all - I can just make the information out on the screen when this happens ?
 
I get a blank screen but doesnt dim if I use any of the buttons, sometimes they work, from time to time I get scrolling odd text. When it goes blank I have to power cycle. The unit still works fine and heats up my water a treat.

I paid via paypal so have just opened up a dispute to heopfully get a reply from SolarImmersion !
 
snipped

5. Once switched on and setup with the various options in the menu - it started to work straight away but I have now noticed the display is now dim and you cant see it as brightly as before - haven't worked out how you constantly brighten the screen yet, but will investigate this later !


Arrrrr - found it !

LCD BACKLIGHT TURNs OFF AFTER 5 MIN TO SAVE ENERGY. TO TURN ON THE BACKLIGHT AGAIN, HOLD ESC BUTTON FOR 1 SEC.
 
I am looking for a solar immersion device but after my fathers bad experience with with the mk2 solar immersion switch and extremely poor customer service (very hard to contact, they did not return calls, generally unhelpful on phone) it has put me clean off this company.He eventually got a replacement box about 2 months later, not for me Im affraid.
 
Here are your choices in no particluar order:
Immersun PV Water Heating, Solar Hot Water Switch and Controller Supplier in Lincolnshire, UK | 4eco Ltd
Wooldrige Solar PV heating switch controller
Solar Immersion SolarImmersion - Surplus Solar Energy Water Heater | (also at Intelligent Solar PV Immersion Heater Switch - Use Surplus PV Power to Heat Water for Marks I and II)
Intelligent Immersion Intelligent Immersion.
Solic 200 Earthwise - SOLiC 200

Not sure if I've left out any other proportional controllers, thes rae the ones I can remember ...
 
I think I am going to hold out for the Immersun mk2, I believe it will be on sale June/July, price dependant I would say this will be the one for me.
 
I think I am going to hold out for the Immersun mk2, I believe it will be on sale June/July, price dependant I would say this will be the one for me.


Unfortunately, I have no 'hands-on' experience of any of the other current market leaders in this field BUT all I will say if they do the job half as good as the SolarImmersion unit - you will be impressed as I've totally turned off my Gas Boiler coming on now as I just dont need it - the water is that hot all day ( ie. normal PV hrs should I say ) - we dont export alot back to the grid anyway ( approx 30-40% ) but this unit is still harvesting that to heat our water - so I am so far, although its early days - VERY IMPRESSED and at such a no frills bargain price, compared to the rest kindly listed by WORCESTER !

Watch this space............. for results ( data, graphs etc ) in the coming weeks !
 
Last edited by a moderator:
I fitted my Immersun early April, and for the month have had totally free hot water, i suspect you have 8 months a year whereby you wont need another source of heating the water, the winter months you just have to have a backup in mind. It is surprising though how little is required to heat a full tank, especially if its just topping up.
 
You're not generating enough then :) :wink:
 
This is true enough- only been able to get the last 12 Sanyos in the country back in Nov/Dec 2011, however i must say you can only work with what you have Worcester and the wife is alao trained well in the art of using all white goods as much as possible in peak times so it works extremely well for us ! :)
 
These look interesting devices - but I'm a bit confused as to how they detect that there's a surplus I thought that a clamp on current detector can't detect direction, so how does the unit "know" that export not import is occurring?
 
Additionally they monitor voltage and phase angle so can get true power figures. It's simples when you know how..
 
Just a little question regarding these Immersun devices. If say I have a 3kw immersion with 1kw available, would I be right in thinking the water wouldn't get as hot or, would it just take longer. In my mind, I'm likening it to a sort of dimmer switch with the bulb only glowing rather than burning brightly.
 
Just a little question regarding these Immersun devices. If say I have a 3kw immersion with 1kw available, would I be right in thinking the water wouldn't get as hot or, would it just take longer. In my mind, I'm likening it to a sort of dimmer switch with the bulb only glowing rather than burning brightly.

It takes longer but our ImmerSuN is giving us a full tank of very hot water pretty much every day. Average day is around midday when it cuts out as the immersion thermostat hits max temp.

Ours was fitted at the start of March and has given a tank of hot water everyday so far except when the snow covered the panels. Two adults one child and enough hot water at night for a bath and showers in the morning before the ImmerSUN starts heating it all up again.

3kw in 1 hour or 1kw for 3 hours still pretty much the same net effect.

cheers

Andy
 
Thanks Andy. Am looking at a tank with twin immersions ( both 3kw ) and wasn't sure whether to change them for lower wattage or not but that clears it up. :)
 
I have a tank with twin 3kw immersions.

The Immersun heats the top element first to basically make sure you have hot water, then moves over to the bottom one and finishes the tank off.

I have found most days if i didnt have a bath today and just used water for washing up and washing etc, it would only need 2-3kw to heat up the following day. 6kw usually does a full tank. If im at home i am finding it hard to resist having my bath a midday and watching it heat it up again :)

Sad but true...............
 
My wife has now complained !!!!!


Apparently the water is too hot now...... LOL

Its set to 60 as well............. you cant please them all, but I'm well impressed even when we aren't producing at max
 
Additionally they monitor voltage and phase angle so can get true power figures. It's simples when you know how..


Yes it works that well that its now far more accurate than the Eon Envir' energy monitor ( clamp) I have, so the consumption figure is showing not as it should - I think this is due to both the clamp used by the Eon device as well as the way our PV is wired up to the tails using a Henley Block and not via the CU. I'm trying to locate a decent energy monitor now to keep up with the Solar Immersions calculations as the DNO meter definitely stops dead, but the consumption fig on the Eon meter doesnt sometimes equal the power generated by the SMA inverter - hence displaying there is a mis-reading somewhere from how I understand the situation...... hence my PVO export figure displayed is incorrect !

But this isnt any fault of the Solar Immersion device which is spot on, its merely too accurate against the consumption meter I decided to utilise !

Just need to work out now what I can use any further surplus on using the 2nd relay which comes as standard :)
 
Here's an example of this as well as it clearly displays how the Solar Immersion 'tracks' your energy generation very closely - the only difference like I said is the Eon monitor's inability to be as accurate as the Solar immersion device;
 

Attachments

  • chart_06052013.jpeg
    28.9 KB · Views: 184
Here's another fine example of great tracking by the Solar Immersion ( ignore the difference as the Eon is not reading correctly and infact the meter is totally stopped dead );

What i want the Eon monitor now to register is what the house is using from both the grid & the PV and NOT what I'm pulling from either or, as like above hardly any electric came from the grid that day ( iirc approx 6kwh ) - it merely as I said showed what the house was using !!!

View attachment 18936
 
Last edited by a moderator:


I've now got another wireless monitor ( a BG one infact ) and the findings from two different tails (+ and - ) are very interesting using both monitors - they both add up to exactly what the SMA inverter is generating, however I now found a way of measuring more accurately the consumption inhouse now...... I dont now why I didnt do or try this before ( possibly due to thinking it would show or be influenced by generation?) , but if I place the Eon Envir' Monitor CT around the AC fed to the PV System ( remember its connected via a Henley Block ) the measurement is nearly bang on....... weird
 
I've now got another wireless monitor ( a BG one infact ) and the findings from two different tails (+ and - ) are very interesting using both monitors - they both add up to exactly what the SMA inverter is generating, however I now found a way of measuring more accurately the consumption inhouse now...... I dont now why I didnt do or try this before ( possibly due to thinking it would show or be influenced by generation?) , but if I place the Eon Envir' Monitor CT around the AC fed to the PV System ( remember its connected via a Henley Block ) the measurement is nearly bang on....... weird


Yes, as I thought - much better monitoring now and this more or less proves it today after the Monitor CT position change;

chart_13052013.jpeg
 
@danesol if that output and some of the others on your pvoutput log are accurate then the Solar Immersion isn't doing a very good job of tracking your generation as it appears to swing wildly either side of the actual generation. If that is the case, your energy consumption for yesterday for example is very worrying.

Unless it is caused by the inaccurate monitoring systems. attached below are your charts for yesterday and today and my chart using an immersun with fall over load for today.

The bottom one is monitored using an eco-eye, mine are monitored using accurately calibrated CT's with AC voltage and phase monitoring also OpenEnergyMonitor.org

It may be just the monitoring, if that isn't accurate then unfortunately you don't really know how well it's performing.

Yours Yesterday:
1-Fullscreen capture 13052013 202358.jpg
Yours Today:
2-Fullscreen capture 13052013 203711.jpg
Mine Yesterday:
2-Fullscreen capture 09052013 235130.jpg
Mine Today (Water hot at 9:45 am) roll over to 750 Watt panel radiator:
1-Fullscreen capture 13052013 204747.jpg
And other one using an ImmerSun (Water hot at 11:30 am)
1-Fullscreen capture 13052013 205538.jpg


The spikes on mine - lots of cups of tea today :)
 
@danesol if that output and some of the others on your pvoutput log are accurate then the Solar Immersion isn't doing a very good job of tracking your generation as it appears to swing wildly either side of the actual generation. If that is the case, your energy consumption for yesterday for example is very worrying.

Unless it is caused by the inaccurate monitoring systems. attached below are your charts for yesterday and today and my chart using an immersun with fall over load for today.

The bottom one is monitored using an eco-eye, mine are monitored using accurately calibrated CT's with AC voltage and phase monitoring also OpenEnergyMonitor.org

It may be just the monitoring, if that isn't accurate then unfortunately you don't really know how well it's performing.

Yours Yesterday:
View attachment 18999
Yours Today:
View attachment 19000
Mine Yesterday:
View attachment 19001
Mine Today (Water hot at 9:45 am) roll over to 750 Watt panel radiator:
View attachment 19003
And other one using an ImmerSun (Water hot at 11:30 am)
View attachment 19004


The spikes on mine - lots of cups of tea today :)



Thanks for that - Yes your right, its still a case of inaccurate/bad monitoring by the Eon Envir monitor - it just cant handle the fact that a Henley Block is involved and I notice some of the 5min interval checks are not quite right - I thought I'd cracked it today but as soon as the Inverter is off the CT belonging to the Eon monitor is showing the total wrong value totally, so the Eon CT is back on the tails supplying to the CU???

However im pleased to say that the CT belonging to the Solar Immersion is spot on and the DNO meter has been completely still until the evening from approx' mid morning. I'm taking regular DNO meter readings to substantiate this. Today I would say we have used 99% of all electric generated as we have only drawn 3kwh overnight and then started to draw again early evening, so although consumption is around 20kwh for the whole day - only around 6-7kwh of that is chargeable from the grid.

I was hoping to know the following but it would seem I might have to forkout for a proper system like you suggested before if I want justification that my immersion device is working in my favour and to keep an accurate record of all events;

1. DNO meter naturally provides us with what we are importing from the utility co

2. Solar PV Meter - gives me an accurate reading for generation

3. Eon monitor - was hoping this could give me a true record of what we are actually using within the home, whether that was from the PV system and/or as top up from the grid but this seems impossible with this Eon unfortunately.
 
Last edited by a moderator:
The EOn monitor (provided by CurrentCost) is notoriosly inaccurate - I was even sent a development system by them and we couldn't get that to work accurately!! Would be out by 25% either way totally inconsistently.

I've got a cupboard full of useless 'free' energy monitors from all sorts of suppliers as I searched for a good one :)

As each CT has been accuratley calibrated, and it monitors the AC voltage and phase angle, my system is within 1% accurate. For instance I've got multiple CT's monitoring the same thing in different places, so it's easy to cross check - e.g. 1 on the Generation (A), 1 on the Consumption (B) and 1 on the DNO supply (C) , my live monitioring system is updated every 6 seconds also calculates B-A and compares it with C, so flagging up if there are any errors - the CT's are also directional (the Current Cost ones arent from what I remember) so I get + and - readings for import/export. My monitor also has nice glowy LCD's that vary from Bright Green (exporting lots) to Bright Red (importing lots :( ) so a simple glance show the current state of generation and consumption.


The problem with 1 and 2 of yours is that they are historical energy meters as opposed to current power meters, amd whilst they are very accurate they will always be out of date by the time you can read them, and they don;t tell you how much of what you've generated you've consumed (you'd need to install either an export meter or total consumption meter for that), and as pointed out above 3 - the Eon monitor is an interesting tool for educating consumers about how much power / energy they are using, that is all it was ever designed for.
 
The BG monitor i've just acquired appears to be the same, but as I said previously when they are both on different tails of the Henley Block - they appear when added together to give precisely the right figure - however I cant export this to PVO :banghead:

So its a case of either getting a suitable monitor of the quality you have or just not bother :shades_smile: but as a techie I doubt I will be able to do that !! LOL
 
I use the eco eye smart PV product as Worcester says above. Running it through COSM to upload into PVO. Recently verified the inverter outputs to the historic data from The Trax software that comes with the smart PV monitor and calibrated out the small variance in totals inverter vs monitor using the PVO formula option.

since doing that three weeks ago the monitor has been 100% accurate to one decimal place for kWh generation so very good IMHO.

image.jpg

My favourite PVO graph so far for obvious reasons and a great example of showing the ImmerSUN tracking the generation. :clap:
 
UPDATE:- Unbelievable for MAY, especially after generation was exceptional for May last year, but I have to report that our particular setup in the NW has had a few days lately where our system just hasnt been able to supply on the whole, enough free electric even to the normal house requirement/useage, so the immersion device hasnt been effective in real terms for those particular days, as it only works with surplus - however that isnt the fault of the device and the HWC has been heated (topped up ) mainly by GAS on those days, however the Solar Immersion has still lived up to expectation where possible, as its continued to use at any point any surplus normally going to the grid as export, keeping export to the grid as close to NIL as possible and this is confirmed by DNO meter readings.

Every little bit helps I suppose......... but substantiates that you really need a backup system on bad weather days IMO
 
Hi everyone,
I've been following this thread with interest as I intend to install a solar immersion (or similar) in the next few weeks. So, just a few questions:-
1. is Solar Immersion a good one to get, or are there better/more reliable ones around now (and if so - how much?)
2. is the discount coupon still valid with the reduced price if £229, or am I just being cheeky here?
3. about how long does it take to install the Solar Immersion?
4. what do people connect as a secondary device - I was thinking perhaps a storage radiator in the hallway for background heating in winter, but I wouldn't need that in summer when there's likely to be a greater surplus. Any suggestions?

I appreciate there are a lot of questions here, but any snippets of information members may be able to offer would be greatly appreciated (i.e. I'm not expecting full answers to every question - just whatever you can offer)

K
 
Hi everyone,
I've been following this thread with interest as I intend to install a solar immersion (or similar) in the next few weeks. So, just a few questions:-
1. is Solar Immersion a good one to get, or are there better/more reliable ones around now (and if so - how much?)
2. is the discount coupon still valid with the reduced price if £229, or am I just being cheeky here?
3. about how long does it take to install the Solar Immersion?
4. what do people connect as a secondary device - I was thinking perhaps a storage radiator in the hallway for background heating in winter, but I wouldn't need that in summer when there's likely to be a greater surplus. Any suggestions?

I appreciate there are a lot of questions here, but any snippets of information members may be able to offer would be greatly appreciated (i.e. I'm not expecting full answers to every question - just whatever you can offer)

K


In answer to above from my prospective;

1. Yes, its a good no frills one, which is working a treat so far but to be fair these types of devices are new to the market in real terms, so it wont be known for a few years how long these devices will last..... watch this space

2. Yes

3. Depends how quick you are :biggrin: but the main time I spent was pulling the cat5 cable through the loft and down the gable end to the DNO meter outside to extend the CT sensor, which has to be on the DNO tails. Wireless CTs would be advantageous, but I would be worried about battery life and wifi/rf reliability ? As I was recently informing someone recently I installed my unit actually in the airing cupboard, so wiring was a doddle, using the existing switched spur and cable to the actual element , which saves messing inside the CU, naturally some may find the reverse better for them.

4. I dont at the moment and I doubt I will as we use the majority of the surplus through home automation and the Solar Immersion, however if we had a larger PV system ( 4Kw ) or didnt use the surplus through the day - I would be looking at this more closely at this, whether that be a storage heater or towel rail. However, it would depend on what you have already in your setting which could be included IMO as buying additional hardware could defeat the financial object but still help your "green" positioning.
 
Contact, I have a home built unit so can’t comment directly but a friend of mine has an Intelligent Immersion i2 and it performs very well with tiny or even zero export, and compared with the Solar Immersion is cheaper, better made, has a 3 year warrantee and a longer track record of reliable operation. Does not have a LCD display but as reported here these displays can give trouble.

Worcester I agree that many energy monitors have poor accuracy. To be fair to them they were not designed to measure the complex waveforms that these types of diverter devices produce. Like you I find the EcoEye Smart PV good but even this is tens of watts out on the grid value, as is my much more expensive Locus system. Only a Fluke wattmeter agrees with my wheel meter.

Danesol, when you say the export is zero, is it really or have you got a wheel style meter that has hit its antireverse stop? On a digital utility meter an export/import of tens of watts takes so long to clock up one pulse/digit change that is can seem more stationary than it really is.

Concerned about the apparent lack of an EMC filter in the Solar Immersion photos above or is it hidden under the LCD? When I asked Solar Immersion about EMC compliance they were pretty vague, just saying it was compliant without stating how and what standard it was tested against. A standard trick is claiming compliance but not mentioning it’s only to the esier to meet industrial EMC standards. Burst Fire units like the Immersun do not need much in the way of a filter but it has light flicker problems. A phase control unit like the Solar Immersion needs a good filter.
 
I installed my Solar Immersion back in March and I have been heating all my hot water by this means since the end of April. My plan was always to hook up a secondary load and last week I added 3 x 300w towel elements and so far they are performing well.
 
snip................

Danesol, when you say the export is zero, is it really or have you got a wheel style meter that has hit its antireverse stop? On a digital utility meter an export/import of tens of watts takes so long to clock up one pulse/digit change that is can seem more stationary than it really is.

Its a 15yr old old style DNO meter and YES it stops dead when there is an equilibrium or if the grid voltage is <= 235vAC it can be seen going backwards on occasion if generation is greater than demand ..............
 
Its a 15yr old old style DNO meter and YES it stops dead when there is an equilibrium or if the grid voltage is <= 235vAC it can be seen going backwards on occasion if generation is greater than demand ..............

That is more like what I experience on my home built unit. Sometimes stopped and sometimes going slowly backwards i.e. exporting say 30W. I doubt anyone will be ever able to achieve completely stopped all the time as varying house power factors and calibration errors make it impossible unless they are using instrument grade measurements of power which these devices can’t do at this price.
 
I also have come fowl of the customer services at solar immersion. I have a faulty unit that I haven't returned yet as I got sick of being passed between technical, returns and sales department. As for the ticket process, needs some improvements
 
I also have come fowl of the customer services at solar immersion. I have a faulty unit that I haven't returned yet as I got sick of being passed between technical, returns and sales department. As for the ticket process, needs some improvements

Whats the problem you have ??
 
Im still trying to get my faulty unit swapped, such a shame a great product is marred by poor customer service.
I agree, purchased mark II last year and never worked, the support is non-existent , they just ignore any message sent to them. Poor customer service.
i would not buy anything else from them, cannot be trusted.
 

Reply to Solar Immersion - my experience ! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
My next job is to install a new Consumer unit for a really fussy customer.........ME! My goto brand is Hager, but will look at others. I also...
Replies
12
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
In addition to the 4 main, well known competent persons schemes (NICEIC, ELECSA, NAPIT and STROMA), there is apparently another, lesser known...
Replies
18
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock