- 272
Anyone got any other solutions for getting from a surface mount socket to surface mount conduit (plastic)
I often have to add a radial spur from a ring main socket.
Assuming I need to retain the double gang 13A outlet I either:
Add a single gang back box next to the double socket.
Stick a Fuse Switched Spur (can be RCD'd if ring final isn't)
Take the output from that to one side in the wall and then out into a conduit terminal box. Then extended the conduit as required.
The other method is to use a surface mounted single gang back box for the FCU and extend the conduit from the side of that. The cable from the double gang 13A coming out into the back of the surface FCU.
Any other neat solutions to get from below surface to over surface conduit?