  1. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    So am i correct than reg 443.4 means unless we provide a risk assesment that states why we are not using a spd in consumer unit changes then we must fit one??
     
    • Agree Agree x 2
  2. Chris Gardner
    Offline

    Chris Gardner EF Member

    Location:
    Leeds
    Business Name:
    Universal AV Services Ltd
    That’s how I interpret it.

    Not sure how you can carry out a risk assessment however because it states that you have to do a calculation with the different lengths of each element of the distributions various cable lengths.

    Lpal, Lpcl, Lpah & Lpch

    Other than asking the DNO not sure how these can be determined.

    So I guess the only real way is to add type 2 devices to each CU adding £200+ to each job?
     
    • Disagree Disagree x 1
  3. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    if only applies to commercial only .
    wait until the Chinese get their act together the price will drop.
     
    • Like Like x 1
    • Disagree Disagree x 1
  4. TonyMitchell
    Offline

    TonyMitchell Electrician's Arms

    Location:
    Berkshire, UK
    443.4 (i) is not commercial only
    "result in serious injury to, or loss of, human life, or"
     
    • Agree Agree x 3
  5. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    How do you come to that.. nowhere do i see commercial only???!!!

    Saw that proteus are now building spd spaces as norm into cu’s.
     
  6. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    those numskulls at the IET ,come up with those ideas .fitting them to a domestic consumer unit it will be like building the ISS .;) [​IMG]
     
    • Funny Funny x 2
  7. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    THAT WHY YOU PUT IN A RCBO. the chances of a spike .you have more chances of being kissed on the lips by a giraffe.
     
    • Agree Agree x 2
    • Funny Funny x 1
    Last edited: Nov 24, 2018
  8. TonyMitchell
    Offline

    TonyMitchell Electrician's Arms

    Location:
    Berkshire, UK
    Buzz - do you mean "by a giraffe?" The giraffe is doing the kissing in this context, isn't he/she/it?
     
  9. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
  10. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    [​IMG]
    read above .;)
     
  11. TonyMitchell
    Offline

    TonyMitchell Electrician's Arms

    Location:
    Berkshire, UK
    The requirements defined by the IET & BSI are what carries weight, not a manufacturer's interpretation...
     
    • Agree Agree x 3
    • Creative Creative x 1
  12. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    An rcbo is not a spd! I dont see a way of ommiting it how the reg is worded
     
    • Agree Agree x 3
  13. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    then I is down to the individual person who make that call.
     
  14. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
  15. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
Loading...
Similar Threads - 18th Forum Date
Cable clips as per 18th edition. Electrical Forum Tuesday at 1:34 PM
Again the dreaded 18th edition additions...AFDDs Electrical Wiring, Theories and Regulations Apr 11, 2019

Share This Page

Users found this page by searching for:

  1. spd 18th edition

    ,
  2. spd risk assessment 18th edition

    ,
  3. spd 18th

    ,
  4. spd 18th edition benefits,
  5. 18 edition reg 443 spd,
  6. 18th edition 443.4,
  7. 18th edition surge protection domestic dwelling,
  8. spd risk assesment
Electricians Directory Post a Domestic Job Post a Commercial Job