I've recently had an electrician round to wire in some new sockets in the bedrooms. While looking at them today I believe he has just spured 1 socket and then spured to the next on the back wall. I can see the cables going from one socket to another so I know it is not tapped of a ring. Is there any situation where having a spur from a spur is OK. There is no fused spur I know this as it goes back to the main board. I picked him has he was registered but I am sure this is not allowed.
 
What is the protective device for the circuit?

If a 32A circuit wired as a ring, in 2.5mm2 cable, then more than one double socket on a spur, and it would be fused down.

But if a 16A or 20A circuit, probably wired as a radial, then it would likely be fine. Or a 32A circuit wired in 4mm2 cable would likely be OK also.

Of course, any new sockets MUST have RCD protection.
 
It's 2.5mm I looks like it's on a 16amp breaker we had the board changed last year. So the board as a rcd covering all sockets. I just thought the regs said you cannot spur from a spur unless it is fused
 
The reason for fusing down on a 32A ring is to protect the cable, 2.5mm2 twin & earth is not rated to 32A. What it is rated to depends on the installation method (buried in plaster, in insulation, etc), but normally it is 20-odd A, and so there is no reason to fuse it down if you already have a 16A MCB protecting the cabling.
 
Yes. If it’s a radial circuit, 2.5mm cable, with a 16A OCPD.

you said the board was changed last year?
could you give us a photograph and say if it’s plastic or metal?
Just curious
 

Reply to Spur from spur in bedroom in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
732
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
I'm sure this question has been asked to death, so apologies! But just wanted some direct confirmation that my intended wiring setup is going to...
Replies
2
Views
3K
I'm sure this has been asked before, but I just want to confirm: Currently I have a spur leaving a socket in the bedroom, into a 13A Switched...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock