Sounds like that guy doesn't know much about electricity or wiring! It's max one double socket off a spur from a RFC, (taking account of cable derating factors such as thermal insulation of course). Any more than that and it has to be a fused spur, as then you could draw more than 26A.
 
HI
you can spur off a ring main as many times as you like provided its fused down... but your limited to 13 amps from the fuse!!

You should have also added, that whilst he can extend as you say, he must also consider the volt drop limitations, which he can calculate, and also ensure that the disconnection times can still be met, and then there is the correction factors for the installation reference method. i suggest he goes back to the painter in question, and tell him that he didn't give him the full info.

Right i am off to change my gas boiler. The window fitter said it was easy, just join the pipes back up, put wet ones to wet ones, dry ones to dry ones and see what happens, apparently if i have got it right it will just work, and if not there will be some sort of bang, but i haven't to be worried about it.
 

Reply to spur off a ring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Why can we use 2.5mm2 for a spur from either the CB or a point on the ring ? Why does this not have to be 4mm2 when using a 32A breaker ?
Replies
13
Views
1K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
679
Can someone explain electrically why we can spur unfused from a ring final on a 32a breaker when the cable is 2.5mm rated at max 27a?
Replies
4
Views
942
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
683

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock