Discuss Why can we spur unfused from rings? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

As bove , the maximum current draw ( in theory ) will only reach 26 amps. but as we all know a 13a fuse will run way over 13amps so in reality its a folly rule but a rule none the less
I'm not so sure it is a folly rule Dusty. I thought the same as you a few years back,.

An MCB (or even more so a fuse), will pretty much run for ever at it's rated current, or even a little above it. Even at say 20% more current running through it, it will still run for quite some time (20% is a guess, just to show the point although I haven't looked at the time/curve graph). I believe BS7671 takes this in to account, so in fact the insulation of the cable can take more than the CCC quoted in BS7671.

In fact, I'll give a proper example.

A 5A BS3036 fuse will take 0.75 secs to blow with 20A of current running through it. If it is wired in 1mm, then the 20A is too much, but I believe the cable would be designed to take this amount of current for (at least) the time given from the time/current graphs.

I would have thought this is the same for a 13A fuse (with slightly different actual figures).

This is a bit of guess work though, and I'm really not sure if it's right. Just seems logical that cable should be designed to take whatever current could be drawn until the fuse blows (as long as the electrician has designed the circuit correctly).
 
I'm not so sure it is a folly rule Dusty. I thought the same as you a few years back,.

An MCB (or even more so a fuse), will pretty much run for ever at it's rated current, or even a little above it. Even at say 20% more current running through it, it will still run for quite some time (20% is a guess, just to show the point although I haven't looked at the time/curve graph). I believe BS7671 takes this in to account, so in fact the insulation of the cable can take more than the CCC quoted in BS7671.

In fact, I'll give a proper example.

A 5A BS3036 fuse will take 0.75 secs to blow with 20A of current running through it. If it is wired in 1mm, then the 20A is too much, but I believe the cable would be designed to take this amount of current for (at least) the time given from the time/current graphs.

I would have thought this is the same for a 13A fuse (with slightly different actual figures).

This is a bit of guess work though, and I'm really not sure if it's right. Just seems logical that cable should be designed to take whatever current could be drawn until the fuse blows (as long as the electrician has designed the circuit correctly).
I agree with what you are saying and several youtube spraks have shown a short bit of 2.5 cable run 50-60 amps before its tarts to get hot,
my point is if you have a ring it should be kept a completed ring , allowing spurs , spider legs and lolly pops you might as well just fit radials in the first place and do away with ring mains
 

Reply to Why can we spur unfused from rings? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Why can we use 2.5mm2 for a spur from either the CB or a point on the ring ? Why does this not have to be 4mm2 when using a 32A breaker ?
Replies
13
Views
1K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
763
Hi! I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock