Discuss Spur off a spur.... make safe with 16A MCB from ring? in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that :eek:

So, question is, if I replace the ring socket (which we don't use) in the house with a small consumer unit enclosure (i.e shower or garage size), with the conservatory connected to a 16A MCB in this, does that make it safe?

Max load we need in the conservatory is 3.4Kw (2Kw heater on the socket nearest to the ring, 1.4Kw heater on the farthest socket), plus a few other low wattage bits like WiFi and a radio. Cabling is 2.5mm.

Follow-up question is, am I right to assume that the CU could be recessed slightly (50mm) into the wall? I know you shouldn't do this with a normal CU, but I am thinking that as it is a steel box and is only carrying ring main it's no different to a normal socket back-box in terms of fire risk.
 
Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that :eek:

So, question is, if I replace the ring socket (which we don't use) in the house with a small consumer unit enclosure (i.e shower or garage size), with the conservatory connected to a 16A MCB in this, does that make it safe?

Max load we need in the conservatory is 3.4Kw (2Kw heater on the socket nearest to the ring, 1.4Kw heater on the farthest socket), plus a few other low wattage bits like WiFi and a radio. Cabling is 2.5mm.

Follow-up question is, am I right to assume that the CU could be recessed slightly (50mm) into the wall? I know you shouldn't do this with a normal CU, but I am thinking that as it is a steel box and is only carrying ring main it's no different to a normal socket back-box in terms of fire risk.
Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that :eek:

So, question is, if I replace the ring socket (which we don't use) in the house with a small consumer unit enclosure (i.e shower or garage size), with the conservatory connected to a 16A MCB in this, does that make it safe?

Max load we need in the conservatory is 3.4Kw (2Kw heater on the socket nearest to the ring, 1.4Kw heater on the farthest socket), plus a few other low wattage bits like WiFi and a radio. Cabling is 2.5mm.

Follow-up question is, am I right to assume that the CU could be recessed slightly (50mm) into the wall? I know you shouldn't do this with a normal CU, but I am thinking that as it is a steel box and is only carrying ring main it's no different to a normal socket back-box in terms of fire risk.
There was reg that allowed a 16a mcb
Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that :eek:

So, question is, if I replace the ring socket (which we don't use) in the house with a small consumer unit enclosure (i.e shower or garage size), with the conservatory connected to a 16A MCB in this, does that make it safe?

Max load we need in the conservatory is 3.4Kw (2Kw heater on the socket nearest to the ring, 1.4Kw heater on the farthest socket), plus a few other low wattage bits like WiFi and a radio. Cabling is 2.5mm.

Follow-up question is, am I right to assume that the CU could be recessed slightly (50mm) into the wall? I know you shouldn't do this with a normal CU, but I am thinking that as it is a steel box and is only carrying ring main it's no different to a normal socket back-box in terms of fire risk.
There used to be a reg that allowed sockets spurred off a ring final to be fed from a 16A mcb.
Suppose it would work subject to volt drop and loop impedance etc.
Regards S.
 
Just recently has some work done on a conservatory, and in the process discovered that the 2 double sockets are not part of a ring main... looks like one is a spur off the back of a ring socket in the main house, and the second is a spur off of that to

So, question is, if I replace the ring socket (which we don't use) in the house with a small consumer unit enclosure (i.e shower or garage size), with the conservatory connected to a 16A MCB in this, does that make it safe?

Max load we need in the conservatory is 3.4Kw (2Kw heater on the socket nearest to the ring, 1.4Kw heater on the farthest socket), plus a few other low wattage bits like WiFi and a radio. Cabling is 2.5mm.

Follow-up question is, am I right to assume that the CU could be recessed slightly (50mm) into the wall? I know you shouldn't do this with a normal CU, but I am thinking that as it is a steel box and is only carrying ring main it's no different to a normal socket back-box in terms of fire risk.
If the two double sockets in the conservatory are spurred from the existing RFC then that is incorrect, unless of course they are being fed via a Spur unit, your best bet would be to contact an Electrician to try and reconfigure the existing RFC.
 
Instead of replacing the socket with a consumer unit why not replace it with an fcu?..
 
Instead of replacing the socket with a consumer unit why not replace it with an fcu?..
Could do of course byt the load may blow the 13 Amp fuse in the FCU the OP stated that the load may be in excess of 3.5 KW I think, 3.4KW to be precise, to close to the limit without doing any calcs.
 
Could do of course byt the load may blow the 13 Amp fuse in the FCU the OP stated that the load may be in excess of 3.5 KW I think, 3.4KW to be precise, to close to the limit without doing any calcs.
D’oh!
I skimmed through that part due to combination of; a long day and Mr San Miguel affecting my attention span
 
D’oh!
I skimmed through that part due to combination of; a long day and Mr San Miguel affecting my attention span
Excuses, excuses, Mate
 

Reply to Spur off a spur.... make safe with 16A MCB from ring? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
865
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock