Hello, I want to install movement sensors where i have my light switches on my staircase. At present i have a two way switches at both the top and bottom of the stairs.
Any advice will be very much appreciated
 
To add to the above, are you intending replace one of the switches with the sensor or add it to the circuit?
 
most sensors like this require a neutral to operate. It may be you don't have one at your switch positions.

Boston? forgive my geographical ignorance, but is that a UK Boston, or the Massachusets Boston?
 
Hi - as mentioned by @littlespark the motion detectors need to be powered (have L and N). This applies wherever they sit and so some new wiring is likely to be needed. One question will be - will you still need the light switches? (for manual over ride say)
 
Could use some ceiling PIRs, then you will have your Neutral.
 

Reply to Stairway movement sensor wiring in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, Some advice would be appreciated… I have 4 downlights in the bathroom and want to add a motion sensor to turn on just one if everything is...
Replies
14
Views
1K
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
426
Hi, I have two 3-way toggle switches by the opposite sides in my garage. Is it possible to replace both of them with motion sensors? Thank you. .grig
Replies
7
Views
386
On either side of my front door is a motion sensor wall light - it looks like both lights operate from one light switch inside the house. The...
Replies
2
Views
1K
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
446

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock