Discuss Stand alone rcd enclosure, metal or plastic in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
168
Hi all; a stand alone RCD enclosure, is this classed as "similar switchgear assemblies" in regards to reg 421.1.201 and so needs to be made of metal ? Im considering that a stand alone RCD and its enclosure might have a different BS number and so might not apply to this reg ? Anyone know, thanks. Its on a TNS system btw.
 
Taken from wiring matters magazine


The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

An example of a similar switchgear assembly is a three phase distribution board that is intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition.

So I would say a plastic enclosure for just an rcd stand alone is the same as a double pole isolator as used by the DNO is not applicable to the regulation.
I know the DNO isolator is outside the scope of bs 7671 but you get my point
 
Due to all the confusion around when Amd 3 came into force, I just started using metal enclosures in the circumstances you describe. An increase in costs, true, but they are generally better/more robust when terminating say 10mm T&E.
 
@ Ian1981... I know the DNO isolator is outside the scope of bs 7671 but you get my point

but is it? may have been fitted by DNO, but if it's after the meter then it's part of the installation and should by covered by BS7671.
 
Due to all the confusion around when Amd 3 came into force, I just started using metal enclosures in the circumstances you describe. An increase in costs, true, but they are generally better/more robust when terminating say 10mm T&E.
Yep I might just get a metal one anyhow, but the insulated wylex ones are so cheap!
I would like to know how it stands with the regs for piece of mind
 
Taken from wiring matters magazine


The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:

Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

An example of a similar switchgear assembly is a three phase distribution board that is intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition.

So I would say a plastic enclosure for just an rcd stand alone is the same as a double pole isolator as used by the DNO is not applicable to the regulation.
I know the DNO isolator is outside the scope of bs 7671 but you get my point

Thanks thats throws some light on the situation but still dont tell you yay or nay !
 
@ Ian1981... I know the DNO isolator is outside the scope of bs 7671 but you get my point

but is it? may have been fitted by DNO, but if it's after the meter then it's part of the installation and should by covered by BS7671.
There's no requirement for said isolator to be in a ferrous enclosure same as the op's stand alone rcd is my point :)
 
Yep I might just get a metal one anyhow, but the insulated wylex ones are so cheap!
I would like to know how it stands with the regs for piece of mind

Yeah, I deliberately avoided answering the question. My take on it is that a non-combustible enclosure is what is intended.
 
welcome to the land of confusion:


oops wrong one.

 
I would use a metal enclosure even though I would not class it as a consumer unit or similar.

If only to prevent somebody after me saying " E shouldn't av dun that it's non compliant that is!"

I wouldn't view it any differently to an FCU, RCD FCU, RCD socket etc.
 
[/QUOTE]I wouldn't view it any differently to an FCU, RCD FCU, RCD socket etc.[/QUOTE]

Thats my view on it too, unless it has something to do with BS numbers
 
Yep I might just get a metal one anyhow, but the insulated wylex ones are so cheap!
I would like to know how it stands with the regs for piece of mind

When this reg came out, Wylex had a series of pics on a pdf, demonstrating their new A3 CU's. Can't found that just now, but here's their vid of their products;

Wylex - http://www.electrium.co.uk/wylex.htm

At 4.06mins you'll see they have a plastic enclosure for an S Type. I queried this topic at the time with my scheme, and their guidance, was in this situation the enclosure should be metal, commenting on Wylex standpoint, saying it doesn't say if that particular install was domestic :rolleyes:

At the time I did ring Wylex technical about their pdf, and was told to speak to their sales, nothing to do with them? So I rang this Wylex sales manager, and asked him why they were suggesting a plastic enclosure could be used in these circumstances, his reply 'Its the lessor of two evils' :D. I've made a comment on the 18th draft, asking to make the definition of 'similar switchgear' clear, clear as a clear thing :praying:

Ooooppps that's 4 paragraphs again teleckky :)
 
How about one of the nice MK 5502s 2 module enclosures, insulated but far less combustible than the usual soft plastic enclosures?
 

Reply to Stand alone rcd enclosure, metal or plastic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
995
My Champion generator is set up (according to the manual) as having a floating neutral. The plan was to run a 16A commando hook up cable from the...
Replies
2
Views
1K
what’s your guy’s opinions on metal panel locks on fibreglass/plastic enclosures. The reason for asking is I’ve seen a few of these enclosures...
Replies
3
Views
722
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
714

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock