I am unable to take global IR readings on a 3 phase consumer unit, i have disconnected the neutral but when i try to measure the meter never settles and eventually times out.
i have tried 2 meter/s with same results
 
Sounds like some power is present even when isolated.

Have you looked to see what sort of volts L+N - E has when isolated? You might also need to put in a small load (1k resistor, or maybe a basic voltage tester in parallel to meter) so you are not seeing low current "phantom" voltages.
 
it seems almost random, put a clamp round the earth found 100mA leakage from lighting circuit,(14 double D fittings
CPCs often have strange currents due to whatever route power from TN-C-S systems is finding back to the substation, etc.

Clamping L&N to get actual leakage is far more useful!
 
Usually i would clamp the L-N but this is 3 phase so that’s quite tricky, the 100mA is only present when the lighting circuit is on ,when turned off it drops to 2 mA ,i have also clamped the cpc from the lighting circuit which confirms 99mA back down it!
 
Unless I'm missing something here or being slow (always an option!!) if you're wanting global IR then just gang the lines together? As for the leakage, 100mA on a large LED lighting circuit doesn't seem implausible, although if that IS the case then it's been poorly designed.
 
Usually i would clamp the L-N but this is 3 phase so that’s quite tricky, the 100mA is only present when the lighting circuit is on ,when turned off it drops to 2 mA ,i have also clamped the cpc from the lighting circuit which confirms 99mA back down it!
OK, that is sounding like a N-E fault somewhere!
 
Finally found the problem , this along with a loose cpc made for a rather dangerous situation on exposed class 1 head height light fittings.

thanks for all the suggestions
 

Attachments

  • A0C9F783-E010-434E-AF26-9F93F975C3FF.jpeg
    150.8 KB · Views: 12
  • 75D7D4DC-F332-4D75-A50E-B9058F96C19D.jpeg
    124 KB · Views: 12

Reply to Strange IR readings on 3 phase board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
284
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
759
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
957
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
600
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock