Thanks everyone for the advice. May I ask, does the termination look ok as there are comments it looks bad, like not great bad or get the dno out to fix it bad.

I’m thinking about asking the Dno to fit an isolator on my side of the meter, can they do that using this cable?
 
That split concentric cable is on your (the outgoing) side of the meter so may well be your responsibility. I've seen it used like that before for sub mains but as has been stated it I would imagine need rcd protection. That is a very rough termination but I have seen worse, as long as the terminals have no signs of arcing I would say it will be ok till you can get someone to look at it! I would get someone local who has a good reputation to take a look before contacting the dno.
I take it your meter is some distance from your consumer unit?
 
The meter is actually outside in one of those boxes normally home to a gas meter, it’s under a raised part of the house so whilst it’s outside, the box is under cover. The cable runs from the box about 30ft round the basement then up to a second 100amp fuse and then into the CU.

Thanks for the help, I’m going to find someone local to Oban who can come and take a look. Not sure how long it’s been like this be the wiring to the house was pretty appalling before it flooded.
 
The most relevant thing is the second 100Amp fuse. If this is a second cutout then all preceeding cabling is likely to be the responsibility of the dno. Do you have a photo of this fuse and does it have a dno seal?
If it looks dnoish then I would call them out for a look see and ask if the installation is compliant under their esqcr regs.
 
It is certainly an untidy job, the cable should be terminated using a 3 finger boot and heat shrink on the conductors.
Connection directly into the meter load terminals should be avoided by fitting a KMF and meter tails /earth to it then connecting the split con to the load side ensuring the split con is adequately cleated.
You may find your other “cut out” is in fact a Red Link rather than another fused cut out to provide a means of isolation albeit single pole.
As it stands the sub main is your responsibility so it may be worth asking if the meter could be moved to your consumer unit position and a double pole isolator fitted between the two.
Looking at the meter it appears well overdue for recertification so request a new meter from your supplier.
 

Reply to Strange Neutral in Armoured from Meter to Henley. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock